    Wiring Jasic 220v line to three prong dryer plug.

    It has the European wiring with the blue, brown and yellow/green wire. I am not able to run a separate line so can I use a three prong dryer plug with no ground? The dryer uses two hots and a neutral with no ground but the welder has a hot, neutral and earth. Am I screwed or can we figure this out? I live in a rental so upgrades are not available.
    CERTIFICATIONS:
    7018M- H.V.O
    10718M- H.V.O
    11018M- H.V.O
    9N10- H.V.O
    71T-1-HYM- H.O.V
    100S1 PULSE ARC 0,035- H.O.V
    100S1 PULSE ARC 0.045- H.O.V
    ER70S-3 PULSE ARC 0.035 H.O.V
    ER70S-3 PULSE ARC 0.045 H.O.V
    ER5554- H.O.V

  2. #2
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    5,248

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Blue and brown as your 2 hot legs

    Yellow/green as your ground*

    In the dryer receptacle/ plug it will be the neutral terminal*
    Last edited by Broccoli1; 06-01-2013 at 02:48 PM.
    Ed Conley
    http://www.screamingbroccoli.net/
    MM252
    MM211
    Passport Plus & Spool gun
    TA 185
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    O/A set
    SO 2020 bender
    Beer in the fridge

  3. #3
    Join Date
    Nov 2011
    Posts
    111

    Re: Wiring Jasic 220v line to three prong dryer plug.

    I am just a little hesitant because instead of having a hot, neutral and ground you would have hot, hot and neutral.
    CERTIFICATIONS:
    7018M- H.V.O
    10718M- H.V.O
    11018M- H.V.O
    9N10- H.V.O
    71T-1-HYM- H.O.V
    100S1 PULSE ARC 0,035- H.O.V
    100S1 PULSE ARC 0.045- H.O.V
    ER70S-3 PULSE ARC 0.035 H.O.V
    ER70S-3 PULSE ARC 0.045 H.O.V
    ER5554- H.O.V

  4. #4
    Join Date
    Nov 2008
    Location
    south GA where its hot in summer and cold in winter
    Posts
    3,636

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Broc is right. You are supposed to have two hots and one ground for your welder. The neutral is only really neutral if you have part of the dryer with a 110 v circuit, otherwise it is probably a true ground.
    Welders:
    Esab Migmaster 250
    Penncraft 230 (oldy but goody)
    HF Plasma 30 (Italian)
    Lincoln Ranger 8
    Smith Oxy/Acetylene/Propane
    Lincoln SA200
    Everlast Power Tig 250 EX
    Everlast PowerUltra 205

  5. #5
    Join Date
    Dec 2011
    Location
    Tampa FL
    Posts
    477

    Re: Wiring Jasic 220v line to three prong dryer plug.

    European wiring blue = neutral, Brown = hot(230v). 3 prong dryer receptacle two hot(110v each) one ground no neutral. I think you would need a transformer to boost the voltage. Also most European equipment is made for 50 hertz and American power is 60 hertz.

  6. #6
    Join Date
    Nov 2011
    Posts
    111

    Re: Wiring Jasic 220v line to three prong dryer plug.

    The welder will work in 50/60Hz so that isn't an issue. Just to make sure we are all on the same page, 220v European power only has one hot. The same style as american 115 but double the voltage. Where as US 230v is two 115v and a neutral with a ground.
    CERTIFICATIONS:
    7018M- H.V.O
    10718M- H.V.O
    11018M- H.V.O
    9N10- H.V.O
    71T-1-HYM- H.O.V
    100S1 PULSE ARC 0,035- H.O.V
    100S1 PULSE ARC 0.045- H.O.V
    ER70S-3 PULSE ARC 0.035 H.O.V
    ER70S-3 PULSE ARC 0.045 H.O.V
    ER5554- H.O.V

  7. #7
    Join Date
    Nov 2011
    Posts
    111

    Re: Wiring Jasic 220v line to three prong dryer plug.

    In other words, it is different than a miller or Lincoln 230v.
    CERTIFICATIONS:
    7018M- H.V.O
    10718M- H.V.O
    11018M- H.V.O
    9N10- H.V.O
    71T-1-HYM- H.O.V
    100S1 PULSE ARC 0,035- H.O.V
    100S1 PULSE ARC 0.045- H.O.V
    ER70S-3 PULSE ARC 0.035 H.O.V
    ER70S-3 PULSE ARC 0.045 H.O.V
    ER5554- H.O.V

  8. #8
    Join Date
    Dec 2011
    Location
    Tampa FL
    Posts
    477

    Re: Wiring Jasic 220v line to three prong dryer plug.

    That is why you need a buck/boost transformer to get 230v on a single line.

  9. #9
    Join Date
    Nov 2011
    Posts
    111

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Quote Originally Posted by leightrepairs View Post
    That is why you need a buck/boost transformer to get 230v on a single line.
    Yea I was afraid of that. Those pigs cost more than the welder.
    CERTIFICATIONS:
    7018M- H.V.O
    10718M- H.V.O
    11018M- H.V.O
    9N10- H.V.O
    71T-1-HYM- H.O.V
    100S1 PULSE ARC 0,035- H.O.V
    100S1 PULSE ARC 0.045- H.O.V
    ER70S-3 PULSE ARC 0.035 H.O.V
    ER70S-3 PULSE ARC 0.045 H.O.V
    ER5554- H.O.V

  10. #10
    Join Date
    Jan 2008
    Location
    Richmond, Virginia
    Posts
    3,184

    Re: Wiring Jasic 220v line to three prong dryer plug.

    If the dryer circuit has only one outlet and goes straight back to a panel where the neutral and ground are bonded, then neutral is the same as ground for the purpose at hand. It's just used for a different purpose with a 120/240V circuit vs a 240V-only circuit.
    "USMCPOP" First-born son: KIA Iraq 1/26/05
    Syncrowave 250 w/ Coolmate 3
    Dialarc 250
    Idealarc 250
    SP-175 +
    TA 161 STL
    Lincwelder AC180C (1952)
    Victor & Smith O/A torches
    Miller spot welder
    Clausing 5904 lathe
    Wells-Index 745 mill

  11. #11
    Join Date
    Mar 2010
    Location
    Delaware
    Posts
    857

    Re: Wiring Jasic 220v line to three prong dryer plug.

    You don't need anything but a PLUG. BLUE HOT, BROWN HOT AND GREEN/YELLOW GROUND there is no NEUTRAL
    Lincoln Power Mig 180C
    Hot Max Spool Gun
    HF 95136 and 60767 Plasma Cutter
    ALPHA TIG 200X
    Lincoln 225 AC
    www.georgesplasmacuttershop.com

  12. #12
    Join Date
    Jan 2008
    Location
    Richmond, Virginia
    Posts
    3,184

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Quote Originally Posted by NHMatt View Post
    ... 220v European power only has one hot....
    Hot just means it's significantly above ground potential. Since we ground in the middle, we have two "half-hots" that are 120V above or below ground. If you ground one side of a 240V transformer, you only have one "hot" that is twice the voltage. Doesn't really matter since it is AC anyway. Electrons don't read code books or pay attention to wiring conventions.
    "USMCPOP" First-born son: KIA Iraq 1/26/05
    Syncrowave 250 w/ Coolmate 3
    Dialarc 250
    Idealarc 250
    SP-175 +
    TA 161 STL
    Lincwelder AC180C (1952)
    Victor & Smith O/A torches
    Miller spot welder
    Clausing 5904 lathe
    Wells-Index 745 mill

  13. #13
    Join Date
    Nov 2011
    Posts
    111

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Sounds good to me. I'll let you know how it welds.
    CERTIFICATIONS:
    7018M- H.V.O
    10718M- H.V.O
    11018M- H.V.O
    9N10- H.V.O
    71T-1-HYM- H.O.V
    100S1 PULSE ARC 0,035- H.O.V
    100S1 PULSE ARC 0.045- H.O.V
    ER70S-3 PULSE ARC 0.035 H.O.V
    ER70S-3 PULSE ARC 0.045 H.O.V
    ER5554- H.O.V

  14. #14
    Join Date
    Nov 2011
    Posts
    111

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Thanks for the help guys. It works beautifully and welds pretty good. It maxes out at 120 and all I had was 1/8" 7018 but cranked all the way it was running hot so I bumped it down to 110 and it was fine. I had 6010 1/8" also that welded fine on about 80 amps. I still need a argon bottle to try the tig and tomorrow I will try the plasma setting. Not bad for $135 bucks at a pawn shop.
    CERTIFICATIONS:
    7018M- H.V.O
    10718M- H.V.O
    11018M- H.V.O
    9N10- H.V.O
    71T-1-HYM- H.O.V
    100S1 PULSE ARC 0,035- H.O.V
    100S1 PULSE ARC 0.045- H.O.V
    ER70S-3 PULSE ARC 0.035 H.O.V
    ER70S-3 PULSE ARC 0.045 H.O.V
    ER5554- H.O.V

  15. #15

    Re: Wiring Jasic 220v line to three prong dryer plug.

    I have the same dilema. So to be clear, did you connect your blue and brown to the two hot leads of the dryer plug? That should give 220V, then which wire did you connect to the green/yellow ground from the welder? The white nuetral or the bare ground wire?

  16. #16
    Join Date
    Jun 2008
    Posts
    137

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Quote Originally Posted by leightrepairs View Post
    That is why you need a buck/boost transformer to get 230v on a single line.
    You cannot create a neutral w/ buck/boost transformers & the machine will not care if it's 240V line to line, or line to neutral.

  17. #17
    Join Date
    Apr 2014
    Location
    Greensboro, North Carolina, United States
    Posts
    348

    Re: Wiring Jasic 220v line to three prong dryer plug.

    The neutral and ground go to the same place. Get a continuity tester and probe neutral bus to ground bus. You will find that there is continuity. The only time this might give you trouble is with a gfci breaker/ recepticle. I know I'm too late and you already figured it out but had to throw in my two cents. I am an American after all
    Thermal arc 211
    Harbor freight 80 amp inverter
    ( rocking the shoulder strap )
    Century 100 amp dc door stop
    Dewalt bandsaw

  18. #18
    Join Date
    Sep 2013
    Location
    clovis, NM
    Posts
    1,134

    Re: Wiring Jasic 220v line to three prong dryer plug.

    In old code 3 prong dryer plug wiring your neutral/ground is the bare wire.

    Green or green+yellow is always non current carrying earth ground as far as I can tell. Some times yellow can be ground or neutral (on some generators).

    I wired in my 220v german microwave, here in the U.S.. Same idea, just smaller wire. Just hooked a blue and brown to the lines and the green/yellow to the bare conductor, via the NEMA 6-15 plug I put on the microwave and 6-15r I put on the wall.
    Cut:
    Miller spectrum 625 - miller lead ground, 10-30p

    GMAW:
    Lincoln SP-135 T, lots of mods + Ar, CO2, He gas mixing cart 0.025 wire
    SMAW:
    Craftsman 230amp AC/DC, miller leads, 10-50p
    Craftsman 100/70amp AC/DC, ducted fan, miller leads, L5-30

  19. #19
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    5,248

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Quote Originally Posted by skid4u View Post
    I have the same dilema. So to be clear, did you connect your blue and brown to the two hot leads of the dryer plug? That should give 220V, then which wire did you connect to the green/yellow ground from the welder? The white nuetral or the bare ground wire?
    We need to know exactly which type of receptacle you have: 3-prong or 4-prong?

    3-prong 120v/240v receptacles used for dryers are strange little beasts because the way they use the Neutral and Ground together. There shouldn't be any bare wire in these receptacles. Since the 3rd wire will carry current it can not be a bare wire and that particular neutral wire goes directly to the main panel.

    4- prong 120v/240v receptacles may have a bare wire for ground because they have a separate wire for neutral.
    Ed Conley
    http://www.screamingbroccoli.net/
    MM252
    MM211
    Passport Plus & Spool gun
    TA 185
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    O/A set
    SO 2020 bender
    Beer in the fridge

  20. #20
    Join Date
    Jun 2008
    Posts
    137

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Quote Originally Posted by Broccoli1 View Post
    We need to know exactly which type of receptacle you have: 3-prong or 4-prong?

    3-prong 120v/240v receptacles used for dryers are strange little beasts because the way they use the Neutral and Ground together. There shouldn't be any bare wire in these receptacles. Since the 3rd wire will carry current it can not be a bare wire and that particular neutral wire goes directly to the main panel.

    4- prong 120v/240v receptacles may have a bare wire for ground because they have a separate wire for neutral.
    3-wire dryer receptacles are non-grounding dual voltage devices, it was allowed prior to the 1996 NEC to ground the frame of dryers to the neutral.

  21. #21
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    5,248

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Quote Originally Posted by Norcal01 View Post
    3-wire dryer receptacles are non-grounding dual voltage devices, it was allowed prior to the 1996 NEC to ground the frame of dryers to the neutral.
    yes- but there shouldn't be a bare wire used, correct?
    Ed Conley
    http://www.screamingbroccoli.net/
    MM252
    MM211
    Passport Plus & Spool gun
    TA 185
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    O/A set
    SO 2020 bender
    Beer in the fridge

  22. #22
    Join Date
    Jun 2008
    Posts
    137

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Quote Originally Posted by Broccoli1 View Post
    yes- but there shouldn't be a bare wire used, correct?
    No, unless SE cable was used & it was run from the service equipment, if it was not run from the service equipment & has a bare conductor it was never compliant w/ NEC requirements. & 2-conductors w/ ground NM cable was never compliant it is always wrong & it does not matter if it was a service panel or sub panel, it's still a sign of bad workmanship.

  23. #23
    Join Date
    Sep 2013
    Location
    clovis, NM
    Posts
    1,134

    Re: Wiring Jasic 220v line to three prong dryer plug.

    Wow that's sad. I think every house I have ever lived in with a dryer hook up all had 2 conductor NM going to them. Even base housing made way after 1996.
    Cut:
    Miller spectrum 625 - miller lead ground, 10-30p

    GMAW:
    Lincoln SP-135 T, lots of mods + Ar, CO2, He gas mixing cart 0.025 wire
    SMAW:
    Craftsman 230amp AC/DC, miller leads, 10-50p
    Craftsman 100/70amp AC/DC, ducted fan, miller leads, L5-30

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
RSS | Home | Penton Media | Contact Us | Subscribe | For Advertisers | Terms of Use | Privacy Statement