    Wiring for lincoln Mig Pak 180

    I just bought a Lincoln Mig Pak 180. The recomended input cable and fuse breaker sizes are as follows:

    Input voltage/frequency = 230 V 60 HZ
    Fuse or breaker size = 40 Amp Super lag
    Input amps = 20
    Power cord = 50 Amp, 250 V, three prong plug, (NEMA Type 6-50P)

    My questions are:
    What size of wire do I need from my service panel wich is at about 45 feet from where I will install my welder's outlet ?

    What does 6-50P means in (NEMA Type 6-50P) ?

    How much wattage is the machine pulling ?

    As I understand I need a cable about 8 gauge with 3 wires. 1 black, 1 white, 1 bare ground
    (8-2)

    The machine will be installed in an attached garage and used for hobby.

    Thanks for your time.

    Claude from Canada.

  2. #2
    Join Date
    Jun 2009
    Posts
    1,525

    Re: Wiring for lincoln Mig Pak 180

    The 8-2 cable you chose would be correct for a US application for a 120v circuit.
    Black—hot
    White---neutral
    Bare-----ground

    In Canada for 230 volts.
    You have two Hot lines and a Ground, no Neutral.
    L1 ------Black
    L2-------Red
    Ground---Green or Green Yellow.

    The 40 amp breaker may be a little over kill but that’s ok. Be sure that the breaker is for 230 volts, two pole.



    Not knowing the length of the cable run it is difficult to say if the gauge is correct.

    Below are some links that will help answer your questions.



    http://www.allaboutcircuits.com/vol_5/chpt_2/2.html

    http://www.stayonline.com/reference-...ght-blade.aspx

    http://images.google.com/images?clie...ed=0CCsQsAQwAw
    Last edited by transit; 12-09-2009 at 12:33 PM.

  3. #3
    Join Date
    May 2008
    Location
    Toronto
    Posts
    400

    Re: Wiring for lincoln Mig Pak 180

    I have Power MIG 180. Sitting on 35A bkr. Never got to max amps. My cable 50ft 10ga. Rubber coat, 3 rubber covered wires. I do not think bare wire would be a good idea. Since bare wire is solid and cable is not flexible enough... So if you go for 8ga - even better - more gages never hurts...

    Total power - look in manual there is something like 18V x 180A, so let say around 4kW...

    Oh yes, about 6-50P - 50 means amps, P-plug, 6- NEMA configrurations. Like 2-prong - numbers 1,2, 3-prong - 5,6... I do not reason for those configuration numbers, but some NEC/NEMA people around here...

    Good luck. Here from Toronto.

    P.S.
    And about attached garage - if it is heated. Say I have attached but use for my car too - tools are rusting.. So would never keep any of my machines in garage... Make sure you do not have any condensation around...
    Last edited by Nomand; 12-09-2009 at 12:44 PM.

  4. #4
    Join Date
    Jun 2009
    Posts
    1,525

    Re: Wiring for lincoln Mig Pak 180

    Sorry, I missed the 45-foot distance.
    The power supply draws 20 Amps at 230 volts, or 4,600 Volt-Amperes.
    If you protect the circuit with a 30 or 35-amp breaker, the online calculators come up with # 12-gauge wire.
    I would use # 10-2 for better performance.

  5. #5
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    6,930

    Re: Wiring for lincoln Mig Pak 180

    Hey Claude,

    In the US the NEC makes allowances for non-continuous duty equipment such as welders. Using the derating factors on can reduce wiring sizes (if you wish) as long as that circuit is specifically dedicated to the type of equipment it was installed for. So here a sweet circuit dedicated to small to medium wleders would be a 30 amp breaker and 10/2 wire just as you described. Black=hot, white=hot, and a bare ground NMC, 230 volt.

    However------------those same allowances may not apply in Canada. You'd really should consult with only those familiar with Canadian regs so you can be up to code or at least 'code like'.
    Last edited by Sandy; 12-09-2009 at 09:34 PM.

  6. #6
    Join Date
    Jun 2009
    Posts
    1,525

    Re: Wiring for lincoln Mig Pak 180

    No sandy, the White wire may not be used as the second leg of a 230 volt circuit, US or Canadian code.

  7. #7
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    6,930

    Re: Wiring for lincoln Mig Pak 180

    Quote Originally Posted by transit View Post
    No sandy, the White wire may not be used as the second leg of a 230 volt circuit, US or Canadian code.
    I should qualify by adding that white may be used only if it is recolored and only in 230 volt circuits not requiring a neutral.

  8. #8
    Join Date
    Nov 2009
    Location
    Arizona
    Posts
    955

    Re: Wiring for lincoln Mig Pak 180

    Quote Originally Posted by Sandy View Post
    I should qualify by adding that white may be used only if it is recolored and only in 230 volt circuits not requiring a neutral.
    And I'd like to add that the exception for re-identifying a white conductor as a hot only applies to cables. Conductors in conduit may not be re-identified. (US)

    Also, that's not really my car.

  9. #9
    Join Date
    Jun 2009
    Posts
    1,525

    Re: Wiring for lincoln Mig Pak 180

    Sandy, re-read links in post # 2 for the Canadian color codes. Ground = Green or Green+yellow.

  10. #10
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    6,930

    Re: Wiring for lincoln Mig Pak 180

    Quote Originally Posted by transit View Post
    Sandy, re-read links in post # 2 for the Canadian color codes. Ground = Green or Green+yellow.
    Right, but I'm not in Canada. That's why I specifically stated "here" as in the US.

  11. #11
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    6,930

    Re: Wiring for lincoln Mig Pak 180

    Quote Originally Posted by bigb View Post
    And I'd like to add that the exception for re-identifying a white conductor as a hot only applies to cables. Conductors in conduit may not be re-identified. (US)

    Also, that's not really my car.
    Your correct on that.

  12. #12
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    6,930

    Re: Wiring for lincoln Mig Pak 180

    Just a side note as to what might be done with the white wire here is the US, not Canada.

    ""In type NM cable, conductor insulation is color-coded for identification, typically one black, one white, and a bare grounding conductor. The National Electrical Code (NEC) specifies that the black conductor represent the hot conductor, with significant voltage to earth ground; the white conductor represent the identified or neutral conductor, near ground potential [9]; and the bare/green conductor, the safety grounding conductor not normally used to carry circuit current. Wires may be re-coloured, so these rules are commonly excepted.[10] In 240-volt applications not requiring a neutral conductor, the white wire may be used as the second hot conductor, but must be recolored with tape or by some other method.[citation needed] Four-wire flexible equipment connection cords have red as the fourth color; unlike European practices, color-coding in flexible cords is the same as for fixed wiring.[citation needed]""

    http://en.wikipedia.org/wiki/Electri...(United_States)


    ""Exception: Conductor identification shall be permitted in accordance with 200.7.
    Ungrounded conductors with white or gray insulation are permitted if the conductors are permanently reidentified at termination points and if the conductor is visible and accessible. The normal methods of reidentification include colored tape, tagging, or paint.""

    From another forum.

    Now back to the thread about wiring in Canada.

  13. #13
    Join Date
    May 2008
    Location
    Toronto
    Posts
    400

    Re: Wiring for lincoln Mig Pak 180

    It seems, guys, you are going crazy about those colours...

    Especially in view of the fact - his cable, the same gauge wires, two hots... From both sides his wiring. As long as he does not betray his principals and follow the same colour scheme in US or Canada - he is OK...
    And again, avoid 10/2... In Home Depot available 10/3 without bare wire all good rubber...

  14. #14
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    6,930

    Re: Wiring for lincoln Mig Pak 180

    [QUOTE=Nomand;339558]It seems, guys, you are going crazy about those colours...QUOTE]


  15. #15
    Join Date
    Jun 2009
    Posts
    1,525

    Re: Wiring for lincoln Mig Pak 180

    [quote=Sandy;339572]
    Quote Originally Posted by Nomand View Post
    It seems, guys, you are going crazy about those colours...QUOTE]

    Yes, there are many work a-rounds. It may be just me, I like to stick to the NEC.

    Who? Me, nuts?

  16. #16

    Re: Wiring for lincoln Mig Pak 180

    Quote Originally Posted by transit View Post
    The 8-2 cable you chose would be correct for a US application for a 120v circuit.
    Black—hot
    White---neutral
    Bare-----ground

    In Canada for 230 volts.
    You have two Hot lines and a Ground, no Neutral.
    L1 ------Black
    L2-------Red
    Ground---Green or Green Yellow.

    The 40 amp breaker may be a little over kill but that’s ok. Be sure that the breaker is for 230 volts, two pole.



    Not knowing the length of the cable run it is difficult to say if the gauge is correct.

    Below are some links that will help answer your questions.



    http://www.allaboutcircuits.com/vol_5/chpt_2/2.html

    http://www.stayonline.com/reference-...ght-blade.aspx

    http://images.google.com/images?clie...ed=0CCsQsAQwAw
    I decided to go overkill and installed it with a cable 8-3 with and a double pole 40 amp breaker. The lenght is 50 feet. I tried it yesterday and it works great, Now I've got some practicing to do!


    Thanks for everybody's coments

  17. #17

    Re: Wiring for lincoln Mig Pak 180

    I have a 180 as well and I ran 3 wire to box. I have tried black L1 red L2 and did not use white,I hooked up the G. But the welder does not turn on. So what do I need to do? Here is what happened when I tested for V.
    BLK to RD no V
    BLK to WHT 120 V
    RD to WHT 120 V
    I don't know what to do with the Wht? It seems to me you have to use Wht to complete the Cir.

  18. #18
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    6,930

    Re: Wiring for lincoln Mig Pak 180

    Both of your 120 volt legs are actually the same 120 volt leg at the breaker box. My guess you've used the wrong breaker style or it is shifted from where it needs to connect. You need 240 volts across the two.
    "The things that will destroy America are prosperity at any price, peace at any price, safety first instead of duty first, the love of soft living and the get rich quick theory of life." -Theodore Roosevelt

  19. #19

    Re: Wiring for lincoln Mig Pak 180

    First post. Hi...
    Just painted the inside walls on the new 20X32 garage/workshop. I had told the electrician I was buying a 180 and it needed 220 - 20 amps. So I now have 2 new outlets wired with 12/2 red wire and a 220/20 amp breaker.

    A few days ago I bought the 180 welder. Read the specs. Joined this forum. Now I'm SOL with my new wiring?

    Can I make a pigtail cord and just make this work?

    Or are:
    The 2 small 2 outlet boxes with a 220/20 receptacles wrong. (not 6-50)
    The wire size (12/2) is wrong.
    The breaker is wrong.

    Should I just install a new 6-50 outlet beside the electrical panel and wire it to a new 220/40 super lag breaker and buy a 25 Ft extension cord?

  20. #20
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    5,230

    Re: Wiring for lincoln Mig Pak 180

    Quote Originally Posted by Rick Hubka View Post
    First post. Hi...
    Just painted the inside walls on the new 20X32 garage/workshop. I had told the electrician I was buying a 180 and it needed 220 - 20 amps. So I now have 2 new outlets wired with 12/2 red wire and a 220/20 amp breaker.

    A few days ago I bought the 180 welder. Read the specs. Joined this forum. Now I'm SOL with my new wiring?

    Can I make a pigtail cord and just make this work?

    Or are:
    The 2 small 2 outlet boxes with a 220/20 receptacles wrong. (not 6-50)
    The wire size (12/2) is wrong.
    The breaker is wrong.

    Should I just install a new 6-50 outlet beside the electrical panel and wire it to a new 220/40 super lag breaker and buy a 25 Ft extension cord?
    What are the 20amp 220v receptacles for? Do you have other tools that will utilize these receptacles?

    If YES, then just leave them and install a 6-50 and run a 25' ext. cord as you mentioned.

    ( you'll probably need an extension cord anyway regardless of which receptacles you use)

    If No, then you can replace the 20amp 220v receptacle with a 6-50r and try running the 180 on the 20amp 220 breaker. The 12/2 wire is protected by the 20amp CB so no worries there. Depending on the type of work you'll be doing with the 180 you may never trip the CB.



    The above will get you up and running quickly. If you find yerself tripping the 20amp breaker then go ahead and run a new circuit as mentioned before.


    making a Pigtail is not out all together but
    Ed Conley
    http://www.screamingbroccoli.net/
    MM252
    MM211
    Passport Plus & Spool gun
    TA 185
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    O/A set
    SO 2020 bender
    Beer in the fridge

  21. #21

    Re: Wiring for lincoln Mig Pak 180

    Thanks for the advice Ed.

    Ok. I'll use the existing 20 amp outlets with 6-50r and see how that plays itself out.
    Hopefully the hydro hookup happens next week and I get to play!

  22. #22

    Re: Wiring for lincoln Mig Pak 180

    hey guys im a newbie here to this site.. but i have a few issues.. just bought a lincoln 180 mig pac.. have it wired like this..
    10 wire breaker is a double 40 amp federal in canada..
    black is to large pin on 6 50r
    red is to other pin on the 6 50r
    and white is to the ground half round pin..
    both red and black are both wired to the double 40 breaker to feed it the required 110 each side.. and the white is grounded..
    so now i tried to turn it on and no juice what so ever..????!!! i then tried to pu the white wire to the nuetral bar but still no go??!!
    so i then re wired the whole gambit and just used the one side of the 40 double breaker and hooked it up just like a regular 110
    black to the 40 breaker only one side used now..
    red to neutral bar and white to ground..

    and it works but dont have enough juice running through it makes a pretty crappy bead and just piles it up not enough heat to melt it.. so...??? does any one have any ideas as to what the hell is going on here is there a problem that im not seeing? ive gone over this alot and ive hooked it up the same way everyone else is saying to with the double breaker and no neutral but it isnt working? help!! haha

  23. #23
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    5,230

    Re: Wiring for lincoln Mig Pak 180

    You need to meter the receptacle to confirm you have 240v there.

    Most likely the breaker it self is not installed correctly and is not getting the 240v from the panel to pass along to the receptacle.

    It can happen.
    Ed Conley
    http://www.screamingbroccoli.net/
    MM252
    MM211
    Passport Plus & Spool gun
    TA 185
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    O/A set
    SO 2020 bender
    Beer in the fridge

  24. #24
    Join Date
    Nov 2009
    Location
    Arizona
    Posts
    955

    Re: Wiring for lincoln Mig Pak 180

    If you are using the Federal 1" breaker you need to stradle one of the little plastic dividers on the bus so that each half of the breaker is in a different square or you will not see 240 volts.
    Miller Challenger 172
    Linde 235 AC Stick
    Victor 100C
    Harris O/A
    Miller Thunderbolt AC/DC 225/150
    Lincoln Weldanpower 3000LX

    No, that's not my car.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
RSS | Home | Penton Media | Contact Us | Subscribe | For Advertisers | Terms of Use | Privacy Statement