    Wiring syncrowave 200 at home

    Getting a Syncro 200. Been using the 250DX at work and loved it. Working with thin to med gauge steel/ aluminum. For the stuff at home wont be going over 70 amps. The welder will be maybe 5 - feet from the box. What the simplest way to hook this up? Our dryer uses a 60 amp but I think thats going to be too low to use. Am I just going to buy a higher amp breaker and branch off the main in the garage? Or could I just use the Dryer breaker? Here are some picks of my box and maybe someone could help with explaining how you all wire these things up. Thanks!

    Name:  1.jpg
Views: 350
Size:  39.4 KB

    Name:  2.jpg
Views: 347
Size:  98.9 KB

    Name:  3.jpg
Views: 347
Size:  27.9 KB

  2. #2
    Join Date
    Feb 2008
    Location
    North of Philly
    Posts
    16,011

    Re: Wiring syncrowave 200 at home

    Our dryer uses a 60 amp but I think thats going to be too low to use.
    60 amp 220v is a bit high for a dryer. Most I've seen are 30 amps. You can run a Syncro 200 on a 50 amp breaker. That's what mines curently hooked into in the garage. So far I haven't tripped the breaker yet.
    .



    No government ever voluntarily reduces itself in size. Government programs, once launched, never disappear. Actually, a government bureau is the nearest thing to eternal life we'll ever see on this earth!

    Ronald Reagan

  3. #3
    Join Date
    Jul 2010
    Location
    Indian Shores Beach - FL
    Posts
    21

    Re: Wiring syncrowave 200 at home

    Looks like you still have room for one more double breaker if you move them all up and reposition one the single breakers on the opposite side.

  4. #4
    Join Date
    May 2008
    Location
    Orange, TX
    Posts
    11,592

    Re: Wiring syncrowave 200 at home

    I agree with DSW. I think you'll find one of those 30A breakers is feeding your dryer and 50A will be plenty for the 70A output you expect to be seeing plus a bunch. If you were anticipating being flat out all the time with it then you might consider a 60A to prevent possible tripping of a 50A as the input requirements for the machine running AC at 150A output is 54A.

    That said though, I've run my 180 SD at max output on AC off a 50A thru a 50' 8/3 extension cord without tripping the breaker so . . .
    MM200 w/Spoolmatic 1
    Syncrowave 180SD
    Bobcat 225G Plus - LP/NG
    MUTT Suitcase Wirefeeder
    WC-1S/Spoolmatic 1
    HF-251D-1
    PakMaster 100XL
    SA-200 Blackface Code# 8638
    Star Jet 21-110

    Two term limit - one in office, one in jail.

  5. #5
    Join Date
    Jul 2010
    Location
    Tioga county, PA
    Posts
    167

    Re: Wiring syncrowave 200 at home

    Quote Originally Posted by 123 View Post
    Getting a Syncro 200. Been using the 250DX at work and loved it. Working with thin to med gauge steel/ aluminum. For the stuff at home wont be going over 70 amps. The welder will be maybe 5 - feet from the box. What the simplest way to hook this up? Our dryer uses a 60 amp but I think thats going to be too low to use. Am I just going to buy a higher amp breaker and branch off the main in the garage? Or could I just use the Dryer breaker? Here are some picks of my box and maybe someone could help with explaining how you all wire these things up. Thanks!

    Name:  1.jpg
Views: 350
Size:  39.4 KB

    Name:  2.jpg
Views: 347
Size:  98.9 KB

    Name:  3.jpg
Views: 347
Size:  27.9 KB
    Here is a good web site for your electrical questions. They have many licensed electricians and electrical engineers to answer you....http://forums.mikeholt.com
    Embrace theTea Party movement. Congress! Restore, Honor, and abide by the Constitution of the United States of America.

  6. #6
    Join Date
    Aug 2010
    Location
    Rochester, NY
    Posts
    123

    Re: Wiring syncrowave 200 at home

    You should still have 4 slots available since it's a 20-30 panel (20 slots, 30 circuits max using tandems), which means you can plug a 2-pole breaker in on top of either column. The other bar is hidden above that top-right breaker.

    From the lack of single-pole breakers, and the large number of 2-pole, I'm guessing you have subpanels someplace, which is probably fed from the 60A breaker. But that's just a guess.

    Your welder has a 54A rating, with (as far as I can tell) 40% duty cycle, so you need 34A conductors (min). You could use 10 gauge THHN in conduit (flex included), which is rated 35A at 75 deg. C, or 8 guage of almost any copper cable or conductor style, which is rated 40A at 60C and 50A at 75C.

    Since the installation instructions mention 8 gauge copper, you should use that. Two conductors plus ground (manual says 8 gauge, though NEC Table 250-95 only requires 10 gauge copper equipment ground for 60A circuit). The manual references Table 310-16, but that's not for grounds. No matter.

    Use a 60A 2-pole breaker, which should be under $20 (probably well under) for a Square D QO series. They're HACR types (special curves for hermetic A/C equipment), which are time delay with a generous time-current curve.

    You won't get a response from Mike Holt's forum, as it's for pros only, and they won't allow a 'how do I ___' post from a DIYer. Just so you know.

  7. #7
    Join Date
    Jul 2010
    Location
    Tioga county, PA
    Posts
    167

    Re: Wiring syncrowave 200 at home

    Quote Originally Posted by tkanzler View Post
    You should still have 4 slots available since it's a 20-30 panel (20 slots, 30 circuits max using tandems), which means you can plug a 2-pole breaker in on top of either column. The other bar is hidden above that top-right breaker.

    From the lack of single-pole breakers, and the large number of 2-pole, I'm guessing you have subpanels someplace, which is probably fed from the 60A breaker. But that's just a guess.

    Your welder has a 54A rating, with (as far as I can tell) 40% duty cycle, so you need 34A conductors (min). You could use 10 gauge THHN in conduit (flex included), which is rated 35A at 75 deg. C, or 8 guage of almost any copper cable or conductor style, which is rated 40A at 60C and 50A at 75C.

    Since the installation instructions mention 8 gauge copper, you should use that. Two conductors plus ground (manual says 8 gauge, though NEC Table 250-95 only requires 10 gauge copper equipment ground for 60A circuit). The manual references Table 310-16, but that's not for grounds. No matter.

    Use a 60A 2-pole breaker, which should be under $20 (probably well under) for a Square D QO series. They're HACR types (special curves for hermetic A/C equipment), which are time delay with a generous time-current curve.

    You won't get a response from Mike Holt's forum, as it's for pros only, and they won't allow a 'how do I ___' post from a DIYer. Just so you know.
    I don't know where you got that from? I posted my questions on there many times. Did you log in and get a password and user name? Did you enter the NEC section? I am not a licensed electrician. And you will find many others who are also not licensed asking questions. They were very helpful to me with wiring in my whole house 12kw genset to code.
    Embrace theTea Party movement. Congress! Restore, Honor, and abide by the Constitution of the United States of America.

  8. #8
    Join Date
    Aug 2010
    Location
    Rochester, NY
    Posts
    123

    Re: Wiring syncrowave 200 at home

    Excerpted from this page on rules, policies, and disclaimers. http://forums.mikeholt.com/about/about_forum.htm

    "* This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice."

    "Do-it-yourselfers
    This is not a site for do-it-yourselfers.
    This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work."


    There is frequent mention of the moderators holding and reviewing posts from new members prior to allowing them through, with the intent of culling the DIY posts. I was just trying to make folks aware that they might not be responsive to such posts.

    And yes, I am a member, and have been for a while, but I design a lot of very large electrically-driven machinery (hundreds and sometimes thousands of hp).

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
RSS | Home | Penton Media | Contact Us | Subscribe | For Advertisers | Terms of Use | Privacy Statement