    12volt to 110/120 volt inveters

    Having problems setting up a battery backup system for my furnace. Have 2 large 12v battery's connected to my inverter connected to my furnace. Furnace error code is open ground or reversed neutral. I checked the inverter shows open ground even with the ground connected to the grounding stake and water pipe!
    This is the second inverter I got took the first one back, second one the same problem. This is a full sign wave inverter because the furnace will not run on my modified sign wave inverter! Any Help out there?
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  2. #2
    Join Date
    Sep 2013
    Location
    Upstate NY
    Posts
    2,418

    Re: 12volt to 110/120 volt inveters

    The inverter's neutral is floating vs. building ground.

    In a properly operating building electrical system ground and neutral are electrically identical. The difference being neutral is the normal return path and ground is the backup/safety path when things go sour.

    Until and unless you get an inverter that allows tying neutral to ground (grid intertie system) you are looking at lots of frustration.

    Research "neutral-ground bonding" associated with portable generators when used in portable applications.
    Be wary of The Numbers: Figures don't lie,. but liars can figure.
    Welders:
    2008 Lincoln 140 GMAW&FCAW
    2012 HF 165 'toy' GTAW&SMAW
    1970's Cobbled together O/A

  3. #3
    Join Date
    Jan 2015
    Location
    Hamilton Ontario Canada
    Posts
    304

    Re: 12volt to 110/120 volt inveters

    Thank You Mike837go. Not what I wanted to hear but puts me in the right direction. Any ideas for an Inverter? this is getting to be a nightmare! :mad
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  4. #4
    Join Date
    Oct 2008
    Location
    New Jersey (yeah it sucks)
    Posts
    697

    Re: 12volt to 110/120 volt inveters

    1:1 Isolation transformer; tied in at the main panel.
    Last edited by Billdacat; 01-11-2017 at 03:12 PM.

  5. #5
    Join Date
    Sep 2013
    Location
    west texas
    Posts
    2,229

    Re: 12volt to 110/120 volt inveters

    You may need a split phase 120/240 volt inverter to get a 0v neutral.
    Problem is most 120v inverters is they run 60v on the hot and neutral, even on the expensive pure sine ones.
    Only problem is the cheapest one worth a damn is over $2,000.

    You would have the same problem if you were using a 120v only producing generator.
    old Miller spectrum 625
    Lincoln SP-135 T, CO2+0.025 wire
    Craftsman 230amp AC/DC and WP-18V torch
    Craftsman 100amp AC/DC and WP-17V torch
    Century 115-004 HF arc stabilizer, now with foot switch!!
    Home made DR44G alternator welder

  6. #6
    Join Date
    Jan 2015
    Location
    Hamilton Ontario Canada
    Posts
    304

    Re: 12volt to 110/120 volt inveters

    Mad Welder The generator produces the same problem it produces 220V but will not run the furnace! but not an inverter generator! Ouch at $2000. that being US$ equal to $3000 CDN$
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  7. #7
    Join Date
    Jan 2015
    Location
    Hamilton Ontario Canada
    Posts
    304

    Re: 12volt to 110/120 volt inveters

    Billdacat Interesting I have a 1 to 1 transformer may try that! Thanks!
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  8. #8
    Join Date
    Nov 2012
    Posts
    566

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by Ypop View Post
    Any Help out there?

    My backup is an old fashioned wood stove! Yes. Even in Florida.


    You DO realize that motors draw SEVERAL times their rated amperage when starting don't you? And I'm guessing that your furnace requires 220/230 VAC. That means that your amperage draw from TWO 12V batteries is going to be at least 10 times what the furnace draws! Even after the motors have started. Long story short, you would need a MASSIVE inverter to start and run your furnace and you'd need a room full of batteries to operate it for more than a few minutes. This is not a good application for an inverter! Buy a generator instead. They will also cope with the start up current much better than an inverter will.

    This would make a great excuse to buy a new Miller Bobcat or Trailblazer!

  9. #9
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    7,074

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by Ypop View Post
    Mad Welder The generator produces the same problem it produces 220V but will not run the furnace! but not an inverter generator! Ouch at $2000. that being US$ equal to $3000 CDN$
    generator probably has floating neutral as well, if it is giving you the same error code.
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    SO 2020 bender
    Beer in the fridge

  10. #10
    Join Date
    Sep 2013
    Location
    west texas
    Posts
    2,229

    Re: 12volt to 110/120 volt inveters

    You would need a bonded neutral-ground 120/240v generator, then unbond the N-G connection for home tie in.
    Nearly all of the smaller generators that only produce 120v power do not have a 0V neutral.

    An isolation transformer could work.

    I put installed my 100,000btu per hour high efficiency condensing natural gas furnace a few years ago, it actually only needed 120v power. I figured as big as it was it had to be 240v. Good thing I read the owners manual before installing it.
    old Miller spectrum 625
    Lincoln SP-135 T, CO2+0.025 wire
    Craftsman 230amp AC/DC and WP-18V torch
    Craftsman 100amp AC/DC and WP-17V torch
    Century 115-004 HF arc stabilizer, now with foot switch!!
    Home made DR44G alternator welder

  11. #11
    Join Date
    Jan 2015
    Location
    Hamilton Ontario Canada
    Posts
    304

    Re: 12volt to 110/120 volt inveters

    Thanks Beoccoli1 that is what I figured too Know of any way around it?
    Would like to just be able to run generator I thought the inverter would be a work around but no go!

    FlaJoe Furnace is 110V ac full load even start up is 5 amps no AC not needed much up here in Canada maybe one month a year so just suffer through it and yes have a fireplace but have to keep feeding it where as the natural gas keeps coming in!
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  12. #12
    Join Date
    Jun 2012
    Location
    Bemidji MN
    Posts
    12,748

    Re: 12volt to 110/120 volt inveters

    At Dad's old house we just had a plug on the furnace. Then when plugged in to something else the house wiring was unaffected.

    I did the same for my wood stove blower. Just unplug and plug in to something else.

    Will that work here?
    Dave J.

    Beware of false knowledge; it is more dangerous than ignorance. ~George Bernard Shaw~

    Airco 300 - Syncro 350
    Invertec v250-s
    Thermal Arc 161 and 300
    MM210
    Dialarc
    Tried being normal once, didn't take....I think it was a Tuesday.

  13. #13
    Join Date
    Jan 2015
    Location
    Hamilton Ontario Canada
    Posts
    304

    Re: 12volt to 110/120 volt inveters

    Sadly No Minnesota Dave furnace is computer controlled for high efficiency but not for running on generators!
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  14. #14
    Join Date
    Sep 2013
    Location
    Upstate NY
    Posts
    2,418

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by Ypop View Post
    Sadly No Minnesota Dave furnace is computer controlled for high efficiency but not for running on generators!
    For the genset (and possibly for the inverter) use the other 120VAC receptacle and install a G-N bonding plug.

    Name:  img1392m.jpg
Views: 169
Size:  23.4 KB

    You'll want to do some more reading on what this accomplishes BEFORE you use it with the inverter. The Genset should be OK with it.
    Be wary of The Numbers: Figures don't lie,. but liars can figure.
    Welders:
    2008 Lincoln 140 GMAW&FCAW
    2012 HF 165 'toy' GTAW&SMAW
    1970's Cobbled together O/A

  15. #15
    Join Date
    Jun 2012
    Location
    Bemidji MN
    Posts
    12,748

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by Ypop View Post
    Sadly No Minnesota Dave furnace is computer controlled for high efficiency but not for running on generators!
    Right, plug it in to the inverter set-up.
    That way it is not tied to the house.
    Dave J.

    Beware of false knowledge; it is more dangerous than ignorance. ~George Bernard Shaw~

    Airco 300 - Syncro 350
    Invertec v250-s
    Thermal Arc 161 and 300
    MM210
    Dialarc
    Tried being normal once, didn't take....I think it was a Tuesday.

  16. #16
    Join Date
    Jun 2009
    Location
    Draper, UT
    Posts
    316

    Re: 12volt to 110/120 volt inveters

    My inverter genset (Yamaha EF3000iSEB) has a separate terminal on the front that is supposed to be tied to earth ground any time the machine is used (I never do though)
    MillerMatic 252, HTP 221 w/cooler, Hypertherm PM45

    "No matter where you go, there you are" [Buckaroo Bonsai]

  17. #17
    Join Date
    Sep 2013
    Location
    Upstate NY
    Posts
    2,418

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by frieed View Post
    My inverter genset (Yamaha EF3000iSEB) has a separate terminal on the front that is supposed to be tied to earth ground any time the machine is used (I never do though)
    Short of OSHA compliance, none of us do.

    However, G-N bonding has to take place somewhere in a business or residential electrical system. In a house or commercial building, the main panel has the bonding. A portable genset (or inverter) powering an appliance or tools over extension cords, will have to have the bonding added.
    Be wary of The Numbers: Figures don't lie,. but liars can figure.
    Welders:
    2008 Lincoln 140 GMAW&FCAW
    2012 HF 165 'toy' GTAW&SMAW
    1970's Cobbled together O/A

  18. #18
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    7,074

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by frieed View Post
    My inverter genset (Yamaha EF3000iSEB) has a separate terminal on the front that is supposed to be tied to earth ground any time the machine is used (I never do though)
    Silly CYA instructions and does not Bond The N & G.
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    SO 2020 bender
    Beer in the fridge

  19. #19
    Join Date
    Sep 2013
    Location
    west texas
    Posts
    2,229

    Re: 12volt to 110/120 volt inveters

    Generator sets that produce 120v power only, typically your smaller ones have the floating neutral and no neutral ground connection.
    Larger portable contractor 120/240v generators usually always have the neutral ground bond.
    To properly tie in a generator it needs to have the neutral ground bond removed, so that neutral current doesn't flow through both the neutral and ground wires to the generator.
    But you are supposed to have a neutral ground bond on these generators for stand alone operation.
    old Miller spectrum 625
    Lincoln SP-135 T, CO2+0.025 wire
    Craftsman 230amp AC/DC and WP-18V torch
    Craftsman 100amp AC/DC and WP-17V torch
    Century 115-004 HF arc stabilizer, now with foot switch!!
    Home made DR44G alternator welder

  20. #20

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by Ypop View Post
    Having problems setting up a battery backup system for my furnace. Have 2 large 12v battery's connected to my inverter connected to my furnace. Furnace error code is open ground or reversed neutral. I checked the inverter shows open ground even with the ground connected to the grounding stake and water pipe!
    This is the second inverter I got took the first one back, second one the same problem. This is a full sign wave inverter because the furnace will not run on my modified sign wave inverter! Any Help out there?
    If it is 120 volts you have to take the neutral from the inverter and make sure you land it on the L2 not the L1 or you will get that code, even using city or municipal power you will get that code.

    Sincerely,

    William McCormick
    If I wasn't so.....crazy, I wouldn't try to act normal, and you would be afraid.

  21. #21

    Re: 12volt to 110/120 volt inveters

    Inverters are supposed to be internally neutral bonded by code.

    Sincerely,

    William McCormick
    If I wasn't so.....crazy, I wouldn't try to act normal, and you would be afraid.

  22. #22
    Join Date
    Jan 2015
    Location
    Hamilton Ontario Canada
    Posts
    304

    Re: 12volt to 110/120 volt inveters

    ok got the furnace sorted out Thank You Every One!
    This worked for the inverter and probably for the Generator as well seeing as it works for campers with the same problem!
    Name:  plug.jpg
Views: 80
Size:  21.5 KB
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  23. #23
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    7,074

    Re: 12volt to 110/120 volt inveters

    Yup

    Good to hear it's all working.
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    SO 2020 bender
    Beer in the fridge

  24. #24
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    7,074

    Re: 12volt to 110/120 volt inveters

    Quote Originally Posted by frieed View Post
    My inverter genset (Yamaha EF3000iSEB) has a separate terminal on the front that is supposed to be tied to earth ground any time the machine is used (I never do though)
    This confooses the ground neutral bond purpose.

    On a generator, the frame is really the "ground"- when ground is mentioned it is not always Mother Earth.

    Driving a ground rod on a generator does NOT bond the Neutral to "ground".

    Clear as mud ?
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Miller 125c Plasma 120v
    SO 2020 bender
    Beer in the fridge

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
RSS | Home | Penton Media | Contact Us | Subscribe | For Advertisers | Terms of Use | Privacy Statement