    VFD Programming help 3 phase drill press conversion

    Have a 220 3 phase motor trying to get working. The wiring is easy. But when I turn it on the motor sounds like its spinning up, but is not moving. Sorta a noisy type of sound, more vibration type of sound. VFD is a cheap A2 series, the typical ones you see on ebay. Went though the programs didn't change much. should I change all hthe 400hz to 60? sems the videos I have watched leave these alone

    If you can offer any assistance that would be great.

  2. #2
    Join Date
    Dec 2015
    Posts
    50

    Re: VFD Programming help 3 phase drill press conversion

    Yes, back the top end setting down to 60 hertz. Run 0-60 to change speed.

  3. #3
    Join Date
    May 2010
    Location
    ct.
    Posts
    1,197

    Re: VFD Programming help 3 phase drill press conversion

    Quote Originally Posted by MountaineerMiner View Post
    Yes, back the top end setting down to 60 hertz. Run 0-60 to change speed.
    That 400hz. may not be the max. speed.
    400 hz. is a common switching for vfd’s.
    Is vfd set to produce 3 phase? Sounds like motor may be
    “single phasing “.
    Miller a/c-d/c Thunderbolt XL
    Millermatic 180
    Purox O/A
    Smith Littletorch O/A
    Hobart Champion Elite

  4. #4
    Join Date
    Dec 2015
    Posts
    50

    Re: VFD Programming help 3 phase drill press conversion

    Quote Originally Posted by jpump5 View Post
    That 400hz. may not be the max. speed.
    400 hz. is a common switching for vfd’s.
    Is vfd set to produce 3 phase? Sounds like motor may be
    “single phasing “.
    Jpump5 May be correct, I am not an EE. My experience has only been running both low and medium voltage motors on VFDs at work. In my personal shop I have numerous Vfd drives, all of which I have set up for 60 hertz max. The only motors I have been around that run on 400hertz are the cheap Chinese spindle motors. I suppose there are other applications that run on 400hertz, I am just not familiar with them.

    My advise to the OP is try setting to 60 hertz and see what happens, my guess is it works , but again jump5 sounds too be much more informed.....

  5. #5
    Join Date
    Jun 2008
    Posts
    209

    Re: VFD Programming help 3 phase drill press conversion

    Was the drive new or used? If used it's time to read the programming manual & check the parameters that have been set by the prior user.