    50 amp 125/250 twistlock ? bonding ?

    I need to be able to run my single phase 230v welder and 110v grinders at a constuction site. Some makeshift telephone poles are bringing in 230v w/ some 6-4 cord with a female 50 amp 125/250 twistlock at its end.

    I'm going to describe my unsure plan and theory on this.

    My welder is 3 wires. I totally understand how to hook my two hot legs up. Now if I run the ground from welder to designated ground on receptacle and having no wire to connect to the nuetral wire on receptacle , welder should work fine as long as the ground is bonded to the nuetral in the panel or wherever this power is coming from. If it's not bonded, welder won't work because elecrticity can't return to complete it's loop. In this case I can switch the ground wire from welder to the nuetral on the female recptacle and complete the loop and welder should work. However I'm now a safety hazard because my welder hasn't a true ground. ????

    It is also my understanding that all homes built in at least last 40 yrs have nuetral and ground bonded in panel. Someone told me that industrial buildings often aren't? ????

  2. #2
    Join Date
    Nov 2006
    Posts
    6,088
    Post Thanks / Like

    Re: 50 amp 125/250 twistlock ? bonding ?

    Quote Originally Posted by 123weld
    I need to be able to run my single phase 230v welder and 110v grinders at a constuction site...

    ...My welder is 3 wires....
    ...Now if I run the ground from welder to designated ground on receptacle and having no wire to connect to the nuetral wire on receptacle , welder should work fine as long as the ground is bonded to the nuetral ...
    If your welder operates on 230v, the load should be connected from line to line, it will operate without a neutral connection. The third wire should be connected to ground, and normally would carry no current.

    The connection to the neutral conductor would be used with a device that operates on 230v; yet also has some 115v circuits incorporated into it. The 230v load would be connected line to line; while 115v is derived from line to neutral. Of course the fourth wire would be ground, and is connected to the ground terminal.

    I believe that the only exception, which is allowed to share ground and neutral on a 230v three conductor cord, is clothes dryer wiring.

    The 110v grinder, of course, would connect line to neutral.

    Be sure to confirm the voltage of that temporary drop.

    Good Luck
    Last edited by denrep; 01-06-2008 at 09:36 AM.

  3. #3
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    9,327
    Post Thanks / Like

    Re: 50 amp 125/250 twistlock ? bonding ?

    If your welder operates on 230v, the load should be connected from line to line, it will operate without a neutral connection. The third wire should be connected to ground, and normally would carry no current.
    Ditto. Hook up your welder like your welder should be, hot-hot-ground. No switching of anything ever. When making up adapter cords wire up everything as per the NEMA/NEC wiring designations and the system will all work out fine.

  4. #4
    Join Date
    Sep 2006
    Location
    Dallas, Tx
    Posts
    414
    Post Thanks / Like

    Re: 50 amp 125/250 twistlock ? bonding ?

    Keep in mind that the ground - green wire - serves only one purpose - to save your life. It is not used to carry current and in the case of a welder, 230 volt, you could cut the ground wire and the welder would not be affected. You would lose the safety feature but the operation of the machine would be unaffected. weldersales

  5. #5
    Join Date
    Mar 2005
    Posts
    420
    Post Thanks / Like

    Re: 50 amp 125/250 twistlock ? bonding ?

    I assume what you are saying is that you will run a 230V welder from the two hot legs (240V) and the 120V grinder from one hot leg and the ground to make 120V.

    This will work, provided the ground is connected to the true neutral at the other end of the supply. I've seen temporary services dedicated to 240V that has a ground that simply goes to a ground rod on the other end and not the true neutral.

    You need to verify what is really on the other end. Another thing- watch out for OSHA! They'll cut your bean bag off if they catch you doing this on a job site!

  6. #6
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    9,327
    Post Thanks / Like

    Re: 50 amp 125/250 twistlock ? bonding ?

    You need to verify what is really on the other end. Another thing- watch out for OSHA! They'll cut your bean bag off if they catch you doing this on a job site!
    From the presentation it sounds like some one else brought this feed in (prime?).. Whoever brought the power in is the one who needs to worry about osha.

  7. #7
    Join Date
    Jul 2007
    Location
    Cape Cod MA
    Posts
    1,082
    Post Thanks / Like

    Re: 50 amp 125/250 twistlock ? bonding ?

    Quote Originally Posted by turboblown
    I assume what you are saying is that you will run a 230V welder from the two hot legs (240V) and the 120V grinder from one hot leg and the ground to make 120V.
    To operate your grinder you use the one hot leg, and the NEUTRAL, not the ground. Using the ground will "work" but is dangerous to OTHERS using equipment on the same system.

    And if OSHA compliance is an issue you also need a GFCI on your ex cords, and fused at max 20A

    Me!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,274,364.27056 seconds with 17 queries