    4-wire power to 3-wire receptacle

    Need to hookup an adapter for temporary jobsite power to Miller Dynasty 200DX. Available is 50-amp, 230-volt, 4-wire receptacle. Welder has 50-amp, 230-volt, 3-wire plug. Should the center pin of the adapter's 3-wire receptacle be connected to neutral (white) or ground (green) or both? Maybe a dumb question, but just want to be safe.

  2. #2
    Join Date
    Jun 2012
    Location
    Laredo + Midland/Odessa
    Posts
    7,132
    Post Thanks / Like

    Re: 4-wire power to 3-wire receptacle

    Quote Originally Posted by ezduzit View Post
    Need to hookup an adapter for temporary jobsite power to Miller Dynasty 200DX. Available is 50-amp, 230-volt, 4-wire receptacle. Welder has 50-amp, 230-volt, 3-wire plug. Should the center pin of the adapter's 3-wire receptacle be connected to neutral (white) or ground (green) or both? Maybe a dumb question, but just want to be safe.
    If you're talking about a 14-50R, then it should go to ground if that is what it is designated on the original plug. Neutral not needed unless you need 120V input power.
    1st on WeldingWeb to have a scrolling sig!



  3. Likes ezduzit liked this post
  4. #3
    Join Date
    Apr 2013
    Location
    Marina del Rey
    Posts
    993
    Post Thanks / Like

    Re: 4-wire power to 3-wire receptacle

    Jobsite receptacle looks like this. Is wired single phase. Ground is outer housing.

    Name:  41avP0g1UKL._SY445_.jpg
Views: 265
Size:  18.0 KB

  5. #4
    Join Date
    Jul 2011
    Location
    Ottawa, ON Canada
    Posts
    137
    Post Thanks / Like

    Re: 4-wire power to 3-wire receptacle

    OP, you are correct that the outside is the ground on that receptacle. I've attached a photo for reference.

    To go from the 50 amp 125/250 twist lock to your 6-50 receptacle you need, you'll connect the ground to ground. X and Y are your power terminals on the plug and receptacle. Ignore the W terminal, that is for the neutral which you won't need.

    I'd make a nice adapter cord, maybe 10' ling with 6awg cable with the right ends for the cable. Then you'll have one for future use. Or, with 10' of cord, you could just keep changing the male end to whatever plug you need. Either way, it's handy to have adapters for different receptacles.

    Sent from my new phone. Autocorrect may have changed stuff.
    If the women don't find you handsome, they should at least find you handy!

  6. Likes ezduzit liked this post
  7. #5
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,897
    Post Thanks / Like

    Re: 4-wire power to 3-wire receptacle

    One best ways is go to Home Depot and look best price in 50 amp.
    I typically use a range plug 4 wire 50 amp (2 wire hot {red & black} wired 1 ground{green} and 1 Natural {white}).
    I can use for everything.
    The 3 wire is 2 hot and ground good welders but if something needs neutral your out of luck.

    Dave

    Quote Originally Posted by ezduzit View Post
    Need to hookup an adapter for temporary jobsite power to Miller Dynasty 200DX. Available is 50-amp, 230-volt, 4-wire receptacle. Welder has 50-amp, 230-volt, 3-wire plug. Should the center pin of the adapter's 3-wire receptacle be connected to neutral (white) or ground (green) or both? Maybe a dumb question, but just want to be safe.

  8. Likes ezduzit liked this post
  9. #6
    Join Date
    Apr 2013
    Location
    Marina del Rey
    Posts
    993
    Post Thanks / Like

    Re: 4-wire power to 3-wire receptacle

    Thanks fellas. Got the job done after wiring it to ground.

  10. Likes Broccoli1 liked this post
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,309,790.94940 seconds with 21 queries