    ESAB ET 220i AC/DC single to 3 phase with rotophase?

    Hello, I was wondering if I could use a 5 hp rotophase to make 3 phase for this machine. I only have 60 amps single, it requires 80 on single. Will it work? It requires 50 amps on 3 phase.

    Or do I have to purchase a buckbooster for my needs?

    Thank you in advance. Gary.
    Last edited by citytrucker26; 12-16-2020 at 09:21 PM.

  2. #2
    Join Date
    Jan 2005
    Posts
    5,184
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase with rotophase?

    Run it on single phase.5 hp rotary will do nothing for it.. I am not sure where you get your specs but 80 amps input is way off base..Unless there is something really wrong with your machine..
    Blue Demon 140 MSI
    Blue Demon 200 AC/DC
    Esab 160i caddy
    Esab CV353
    INE 1500
    Lincoln 250 Idealarc
    Thermal LM-200
    Thermal 60i- 3phase
    Thermal 15c
    Topshak 40 plasma
    Miller Regency 200/LN-72
    Viking 250 mig/2410 feeder
    Weldcote 140

  3. #3
    Join Date
    Apr 2015
    Posts
    13
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase with rotophase?

    I am just going by whats in the book for power supply.

  4. #4
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase with rotophase?

    Quote Originally Posted by citytrucker26 View Post
    Hello, I was wondering if I could use a 5 hp rotophase to make 3 phase for this machine. I only have 60 amps single, it requires 80 on single. Will it work? It requires 50 amps on 3 phase.

    Or do I have to purchase a buckbooster for my needs?

    Thank you in advance. Gary.
    I think someone put something in your drink.

    Not sure what specs your reading but it requires nothing close to what you have posted.

    The machine is 220 amp. It won't use over 35 on single phase. #8's on a 40 amp breaker feeding a 50 amp 6-50r is more than that machine will ever need.



    Last edited by danielplace; 12-17-2020 at 08:03 AM.

  5. Likes Broccoli1 liked this post
  6. #5
    Join Date
    Apr 2015
    Posts
    13
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    Page 3-2 table 3-1
    1 PH. 3PH.
    208VAC. 100A. 60A
    230VAC. 80A. 50A
    460VAC. 50A. 30A

    I don't know how to upload pictures otherwise I would just take one of the manual that came with it. I just typed it. So your telling me ESAB manual is wrong ? I am going to hook it up and see what happens.

    I have 3awg on a 60 breaker with slow fuse shut off for supply. Over kill yes. For the big millers, not enough.

    I have a big 320AB/p that throws the breaker (60a) at 80 amps AC tig with HF. Thats the reason I got this welder. I hope it works out. I thank you for the info.
    Last edited by citytrucker26; 12-17-2020 at 08:22 PM.

  7. #6
    Join Date
    Apr 2015
    Posts
    13
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    https://flic.kr/p/2khYLY9

    Link to photo of the page
    Last edited by citytrucker26; 12-17-2020 at 08:32 PM. Reason: Link to a photo

  8. #7
    Join Date
    Jan 2005
    Posts
    5,184
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    I run mine on single, and 3 phase with a 15 hp rotary. You will fine on single phase, it will tig weld on a 30 amp 240 volt breaker all day at 200 amps output..
    Blue Demon 140 MSI
    Blue Demon 200 AC/DC
    Esab 160i caddy
    Esab CV353
    INE 1500
    Lincoln 250 Idealarc
    Thermal LM-200
    Thermal 60i- 3phase
    Thermal 15c
    Topshak 40 plasma
    Miller Regency 200/LN-72
    Viking 250 mig/2410 feeder
    Weldcote 140

  9. #8
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    Quote Originally Posted by citytrucker26 View Post
    Page 3-2 table 3-1
    1 PH. 3PH.
    208VAC. 100A. 60A
    230VAC. 80A. 50A
    460VAC. 50A. 30A

    I don't know how to upload pictures otherwise I would just take one of the manual that came with it. I just typed it. So your telling me ESAB manual is wrong ? I am going to hook it up and see what happens.

    I have 3awg on a 60 breaker with slow fuse shut off for supply. Over kill yes. For the big millers, not enough.

    I have a big 320AB/p that throws the breaker (60a) at 80 amps AC tig with HF. Thats the reason I got this welder. I hope it works out. I thank you for the info.


    I found that.

    Not sure why a 220 amp Esab inverter needs twice what a Dynasty 280 amp inverter runs fine on. I guess inrush to charge caps but don't think you need full wire size to match those oversized fuses especially if just for inrush. That is over pretty quick.

    Honestly I was going by my Dynasty 280 thinking if it can run on 33 amps surely a 220 amp can be pulling any more. Then I look at the specs I posted. Seems like 35 or 40 should do it.

    The startup design must be way different than a Miller.

    Am I missing something in the specs listed that would say that machine needs 80 amps. That is outrageous for a 240 volt 220 amp inverter.

    Certainly do not need more than #8 but if it were myself I recon I would put #6's to a 6-50R outlet use that for power and you will have plenty of headroom and use the 80 fuses as just to fire the machine initially.

    Did you see a wire size recommended for that 80 amp fused circuit ?

    If it says so I guess but that seems like way too much for that machine. Even if it needed 80 to start that would only need approx #6's when you figure duty cycle of machine as the NEC allows in a welding power supply circuit. They are doubling the needed amps it says 200%(for startup) so you need 40 amp wire I would think. That is #8's but #6 better especially if doubling the fuse size seems smart to do.

    They are going to specify amperage fuses they should give a hint to consumer of the best appropriate wire size. Running wire good for 80 amps would be unnecessary to say the least.
    Last edited by danielplace; 12-17-2020 at 11:10 PM.

  10. #9
    Join Date
    Jan 2005
    Posts
    5,184
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    Mine starts up just fine on a 20 amp 240 volt line It crazy to worry about something that will never happen.
    Blue Demon 140 MSI
    Blue Demon 200 AC/DC
    Esab 160i caddy
    Esab CV353
    INE 1500
    Lincoln 250 Idealarc
    Thermal LM-200
    Thermal 60i- 3phase
    Thermal 15c
    Topshak 40 plasma
    Miller Regency 200/LN-72
    Viking 250 mig/2410 feeder
    Weldcote 140

  11. #10
    Join Date
    Jul 2018
    Location
    Cumbria, UK
    Posts
    2,221
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    It's a Lorch-based machine, they're very, VERY efficient for the input amps. Ignore what the book says, it's way too conservative, and is rated on stick welding, not TIG.

    You'll run TIG on a 30 amp 230v service all day long, every day, at max amps, and it won't complain!

    For reference, my HT200 (same architecture) runs 200 amps out, at 19 amps input 240v on TIG (in the book). It's hardly going to take an extra 10 input amps to jump to the last 20 amps of output.
    Last edited by Munkul; 12-18-2020 at 03:58 AM.

  12. #11
    Join Date
    Apr 2015
    Posts
    13
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    Quote Originally Posted by Munkul View Post
    It's a Lorch-based machine, they're very, VERY efficient for the input amps. Ignore what the book says, it's way too conservative, and is rated on stick welding, not TIG.

    You'll run TIG on a 30 amp 230v service all day long, every day, at max amps, and it won't complain!

    For reference, my HT200 (same architecture) runs 200 amps out, at 19 amps input 240v on TIG (in the book). It's hardly going to take an extra 10 input amps to jump to the last 20 amps of output.

    Thank you kindly sir. Have a nice weekend.

  13. #12
    Join Date
    Mar 2010
    Location
    Ceres, California
    Posts
    4,233
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    The effective line current is only 27 amp on 230 volts. Go look at the specs page 2-3.
    The way I read the table you found is. minimum building size entrance. the service disconnect fuse size is from the table on 2-3. Read the fine print around the tables on both pages. I found on line this manual.
    Issue Date: October 26, 2016 Manual No.: 0-5346

  14. #13
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: ESAB ET 220i AC/DC single to 3 phase

    Quote Originally Posted by citytrucker26 View Post
    Thank you kindly sir. Have a nice weekend.
    Curious what wire size was the factory installed cable on the machine ?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,281,604.72739 seconds with 18 queries