    May 2010
    Just wiring my garage for 230 volt welder plug, using 6-50, 230V receptical and 50 ft. 6-2 WG wire and a 50 amp breaker from 200 amp panel box in the house with a 4 wire overhead service wire coming from a main disconnect box on a may pole, after the meter and main service. My question is: Is this the right wire to use? The wire has 2 -6 AWG feeds and 1- 10 AWG bare ground. Seems like the ground should be 6 - AWG also.
    I will be connecting the ground into the ground bar and not the netural bar in the panel box since I beleive that the ground bar is not bonded to the netural bar. I will be running a Power Kraft 295 / 64.7 amp buzz box. Thanks for any reply.
    May 2010
    Murray KY
    Re: Does ground AWG size matter?
    How long is your wire run from the breaker box.
    If you need 65 amps for the welder why not do the wiring to meet that spec?
    May 2010
    50 ft., The welder is an old Mongomery Ward Power Kraft 295 AMP. It states that the pri amp is 64.7, but I don't think I would ever use that amperage since I would not be burning with it or welding thicker metal. I also have a brand new Millermatic 211 mig set -up to use,but only 1 welder will be used at anytime on the same plug.
    May 2010
    Murray KY
    The one at at time works well. I think I will just put in a 60 amp breaker and wire like it was for a kitchen electrical range when I get to that point. 50 foot is a short run for many shops.
    Ceres, California
    The hot wires and the neutral carry current and must be the same size. The ground wire is some times one size smaller and must not carry current. Its job is to take stray voltage to ground so we do not get shocked from the case. The second job is to be big enough to make sure the circuit breaker trips. When a hot wire shorts to the case, with out melting in two and starting a fire. This is why I never trust a metal conduit as ground. I always pull a wire for ground. I have seen conduit come apart and now you have lost your ground.
    Dec 2009
    Texas
    Quote Originally Posted by HellDyce View Post
    Correct! Never attach your ground to the neutral bar.
    Aug 2008
    Quote Originally Posted by joedirt1966 View Post
    Unless, of course, you happen to be the power company pole and meter install dudes. Show me a meter not grounded to neutral in this area and I'll eat your hat.
    Just recapping an old argument from the past
    I HATE ELECTRICAL STUFF
    http://www.farmersamm.com/
    Dec 2009
    Texas
    Quote Originally Posted by farmersamm View Post
    Show me someone who connects a welder directly to a live meter and I'll show you an idiot (possibly a dead one).
    P.S. I understand your point about meters but it's not advisable for the original posters intent.
    Mar 2009
    Central Oregon
    Actually the neutral wire does not always have to be the same size as the "hot" or ungrounded size wire, and the ground is sometimes more than one size smaller.
    Millermatic 252
    "Don't worry, he's got a welder, he can fix anything"
    Oct 2009
    Jacksonville Fl
    According to my Electrical Reference guide:
    The MINIMUM size equipment grounding conductors for grounding raceway and equipment is:
    30 amp to 60 amps will require a #10 COPPER grounding wire.
    100 Amp # 8 Copper wire
    200 Amp # 6 Copper wire
    Oct 2007
    Irvine, CA
    IIRC the ground only carries current in the event of a short to ground, hopefully that will cause the breaker to trip. The ground should never need to carry continuous current, so unless it melts in under 3 seconds of being live it will be fine as the breaker will trip.
    May 2010
    Thank you, for your answers. I now have it installed. I did a little reseach at the meter and disconnect box located on the may pole away from the house. I found that the ground was bonded there inside the disconnect box. That means that the panel box in the house is really a sub panel and it has a seperate ground bar located in there. This is where I grounded the welder circuit.
    I have decided to sell the older dinosaur buzz box and buy a newer AC/DC welder since I found out from another forum member that it may not even turn on with only a 50 amp CB. I can still use my Miller 211 on this circuit until I find a newer stick welder.
Page generated in 1,624,374,136.75888 seconds with 11 queries