    I have a 200amp main service panel in the house and want to run a 20-30 ft wire from the spare breakers to a welding plug for a Lincoln 225 TIG/Stick welder.
    What size wire do I need and what breaker size should I use? 8 AWG and 50amp?
    Any help thanks.
    ~Stan

  2. #2
    Join Date
    Jan 2006
    Location
    San Francisco Bay Area
    Posts
    993
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    The manual for the machine will tell you the recommended wire size for various length of run and the recommended breaker rating. Lincoln (and Miller) provides manuals on their website for downloading. You really should have the manual for your welder on hand anyway. www.lincolnelectric.com. Click on products, then operator manuals. Have the code number of your machine on hand.

    awright

  3. #3
    Join Date
    Sep 2010
    Location
    near belleville Ontario
    Posts
    20
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    No manual. It's a very old machine.
    I'll look for a model number on the machine and try to find a manual on-line.

  4. #4
    Join Date
    Aug 2010
    Location
    Rochester, NY
    Posts
    123
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Look for a plate with line voltage and amperage, and if possible, the lowest duty-cycle. You can use the duty cycle and rated current to 'undersize' the branch circuit conductors, but you don't have to. But you should at least have the rated current from the nameplate to size the branch circuit conductors.

    Of course, if it does have a nameplate, it should have the model number on it somewhere, and a call to Lincoln will enable them to fill in the blanks for you, and probably source a manual for the machine, too.

  5. #5
    Join Date
    Nov 2010
    Posts
    73
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    What type of plug does it have? Can you identify it from this photo?

    http://www.nooutage.com/images/nema-config-1ph-250v.gif

  6. #6
    Join Date
    Sep 2010
    Location
    near belleville Ontario
    Posts
    20
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Thanks Aw & TK. Some good advice to look for.
    Thanks for the chart too Joisey.
    I'll check it all out and post my results.
    Just hope the feed wire isn't too too much money.
    I'd like to set up the welder finally.
    Thanks again guys.
    ~Stan

  7. #7
    Join Date
    Jan 2004
    Location
    Las Vegas, NV
    Posts
    3,174
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    50A 2-pole 240V breaker and minimum #12 wire. The smaller wire is perfectly fine because this machine has a 20% duty cycle. There are thousands of these installations all across the country.

    Many opt for larger wire, but that is completely up to you. You need three wires: two hots and a ground. If you use NM cable (Romex) that would be 12/2, 10/2, or 8/2, etc, as they don't count the uninsulated ground in the wire count for the cable.

    If it has the standard welder plug (as it did when it was new) you will need a NEMA 6-50R receptacle.

    I do this for a living.

  8. #8
    Join Date
    Nov 2010
    Posts
    73
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    you cant run 50A on #12 wire legally per NEC. You need #8 for copper wire if your circuit protection is 50A.

  9. #9
    Join Date
    Jan 2004
    Location
    Northern Cal., Shasta County
    Posts
    9,327
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    There's a derating factor allowable for circuits which feed only welding equipment. The derating (downsizing of the wire) is based on the duty cycle of a particular piece of equipment or model.
    "The things that will destroy America are prosperity at any price, peace at any price, safety first instead of duty first, the love of soft living and the get rich quick theory of life." -Theodore Roosevelt

  10. #10
    Join Date
    Nov 2010
    Posts
    73
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Sandy, can you give me the code reference for that so I can read up?

  11. #11
    Join Date
    Aug 2010
    Location
    Rochester, NY
    Posts
    123
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Quote Originally Posted by joiseystud View Post
    Sandy, can you give me the code reference for that so I can read up?
    NEC Art. 630, specifically 630.11(A) for individual welders, used with Table 630.11(A) which is the circuit uprating multipliers based on welder duty-cycle.

  12. #12
    Join Date
    Nov 2010
    Posts
    73
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    thanks for the info. My suggestion is unless this is being hardwired that the normal sizing practice be used. Its just easy to think that some day someone might mistake that ckt for a 50A ckt and overload it with something else. Also i think if you ever see the chance that you would use plasma on that ckt the derating goes out the window. I will set mine up with two receptacles on 1 ckt with both plasma and welder connected this way i can cut for however long I want then go right to welding withing taking the time to let the wires cool.

  13. #13
    Join Date
    Sep 2011
    Posts
    6
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    I wonder if anyone can help here. Im new to welding , i have a lincoln 225 stick welder. I have installed a 50 amp breaker in the fuse panel, i have 200 amp service in the garage where the welder is located, and i have run 10/2 wire from the panel. The penetration into the metal is not as good as it should be......Have i missed anything?

  14. #14
    Join Date
    Feb 2008
    Location
    North of Philly
    Posts
    20,159
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Brownie check to see what the voltage is at the panel and at the plug between the two hot leads. It should be the same at both and about 230v give or take about 10 volts. Since it sounds like the machine welds, I'd guess the voltage is good and your input is not the issue here. Usually if you have the machine wired wrong it simply will not work.

    My guess is that your issue is with something else, like your technique or your rod choice. If this is the case you'd be best off starting a new thread to ask questions rather than using this one. Post up as much info as possible so we can help. Amps you have the machine set at, Ac, Dc+ or Dc-, Rod being used and size, material thickness, rod angle, arc length, travel speed ( how much weld you got out of one rod is a good idea of speed) and so on... the more info you give the better we can help. Also don't forget to post picts so we can see the issue you are having. "lack of penetration" doesn't mean much in itself, but that with a few picts can explain a lot more.

    I can think of any number of common newbie mistakes with stick that would cause your issue of "lack of penetration". With the info above we can help get you going in the right direction.

    Good luck.
    .



    No government ever voluntarily reduces itself in size. Government programs, once launched, never disappear. Actually, a government bureau is the nearest thing to eternal life we'll ever see on this earth!

    Ronald Reagan

  15. #15
    Join Date
    Sep 2011
    Posts
    6
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    I went to home depot to talk to someone about this. I think ive solved the problem. I switched to 8/2 wire with a 50amp breaker for the panel.... He seems to think the way i had it before, not enough current was getting through to the welder, therefore thats the reason i was only getting sparks and a bit of surface weld, but not anything that would actually hold as a proper weld . Thanks for your reply, and ill keep you posted!!!

    Cheers,

    Brownie

  16. #16
    Join Date
    Sep 2011
    Location
    Da UP
    Posts
    210
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    is that 30' before or after all the twists and turns?

    6 gauge would be the best, but you could probably squeak by with 8.

    don't forget to put it in conduit if it is not in the studs.

  17. #17
    Join Date
    Sep 2011
    Posts
    6
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Im confused here..... Ive got everything wired ok here i think....
    Ive got 8 guage wire, red and black wires to the plug, ground as well. White wire taped off.
    To the panel,
    I have double pole 50 amp breaker , incoming the panel says 200, ( i assume its 200 amp) The red and black wires from the plug are attached. Ground to the panel bar , white as well.
    Ive checked the plug , there is power to it, yet the welder will not turn on. At first i thought it was the welder ( Lincoln ac225) but after trying it out at work, it works fine.....cant seem to figure out why it wont work at home.......Anybody???

  18. #18
    Join Date
    Sep 2011
    Location
    Woodsfield, Ohio
    Posts
    341
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Try spreading or pinching the pins on the plug. Not making good contact inside the power receptacle. Common problem, cheap Chinese junk, more so. Usually get it with 115 VAC but is possible with 220 VAC.

    About all it can be if you have proper power at the receptacle and welder works at a different source.

  19. #19
    Join Date
    Sep 2011
    Posts
    6
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Ill give it a shot....hope it works.... very frustrating ! haha. thanks for the reply, ill keep you posted...Cheers!

  20. #20
    Join Date
    Mar 2010
    Location
    Delaware
    Posts
    2,975
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    The Lincoln AC225 calls for a minimum 40amp circuit ( chart is for copper wire )

    Rated Ampacity Wire Gauge
    10 Amps 18 Gauge
    13 Amps 16 Gauge
    15 Amps 14 Gauge
    20 Amps 12 Gauge
    30 Amps 10 Gauge
    45 Amps 8 Gauge
    60 Amps 6 Gauge
    80 Amps 4 Gauge
    100 Amps 2 Gauge
    150 Amps 1/0 Gauge
    200 Amps 2/0 Gauge
    www.georgesplasmacuttershop.com
    Plasma Cutter and Welder Sales and Repairs--Ebay store
    Tec.Mo. Dealer Consumables for the PT and IPT torch's

  21. #21
    Join Date
    Nov 2009
    Location
    Arizona
    Posts
    3,583
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Quote Originally Posted by Brownie View Post
    Im confused here..... Ive got everything wired ok here i think....
    Ive got 8 guage wire, red and black wires to the plug, ground as well. White wire taped off.
    To the panel,
    I have double pole 50 amp breaker , incoming the panel says 200, ( i assume its 200 amp) The red and black wires from the plug are attached. Ground to the panel bar , white as well.
    Ive checked the plug , there is power to it, yet the welder will not turn on. At first i thought it was the welder ( Lincoln ac225) but after trying it out at work, it works fine.....cant seem to figure out why it wont work at home.......Anybody???
    What brand is your electric panel and is your two pole breaker one inch wide or two inches wide?
    Miller Challenger 172
    Miller Thunderbolt AC/DC 225/150
    Miller Maxstar 150 STL
    Victor 100C
    Victor Journeyman
    Oxweld OA
    Harris O/A
    Smith O/A little torch

    No, that's not my car.

  22. #22
    Join Date
    Sep 2011
    Posts
    6
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    By the chart you sent, i think the wire is correct, i have a 50 amp breaker, bought at home depot, a stablock panel .....breaker is double pole, total width is about an inch.

  23. #23
    Join Date
    Nov 2009
    Location
    Arizona
    Posts
    3,583
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    Quote Originally Posted by Brownie View Post
    By the chart you sent, i think the wire is correct, i have a 50 amp breaker, bought at home depot, a stablock panel .....breaker is double pole, total width is about an inch.
    You will notice in your Stab-Lok panel the buss is made up of one inch squares separated by plastic dividers. You must put the two pole breaker in so it straddles one of the plastic dividers, so half of it is in one square and half in another, or you will not get 240 volts. In other words, move it up or down 1/2 space.
    Miller Challenger 172
    Miller Thunderbolt AC/DC 225/150
    Miller Maxstar 150 STL
    Victor 100C
    Victor Journeyman
    Oxweld OA
    Harris O/A
    Smith O/A little torch

    No, that's not my car.

  24. #24
    Join Date
    Sep 2011
    Posts
    6
    Post Thanks / Like

    Re: Want to wire for a Lincoln 225 amp welder:

    I think thats what the problem is.....( or at least i hope so ) haha.
    I will try that . It does make total sense!!! . Ill keep you posted
    Thanks a lot boss

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,286,036.90351 seconds with 20 queries