    Re: How should I run 220 to my shop?

    Quote Originally Posted by GiantTechGuy View Post
    ...if he's just trying to get a 220 receptacle installed...
    Come on!

  2. #27
    Join Date
    Nov 2007
    Location
    New Hampshire
    Posts
    425
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by GiantTechGuy View Post
    Services and feeders are not sized by simple addition of all the loads,other factors are involved. So you may think just because its a 50 amp panel that you are limited to this load at 20 amps and that load at whatever and now you have exceeded the 50.
    But you very well may not have exceeded it.
    http://www.PlasmaMetalCutter.com

    GiantTech Cut40D
    GiantTech Cut50D
    GiantTech CT520D
    GiantTech Tig200s
    GiantTech Arc200
    GiantTech Tig200PACDC
    Miller MM210
    No Brand Chinese Chop Saw
    No Brand Chinese 4" Angle Grinder

  3. #28
    Join Date
    Nov 2007
    Location
    New Hampshire
    Posts
    425
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by ezduzit View Post
    Come on!
    Again... if money is an issue. I repeat I am not against installing a larger feed. COME ON !
    http://www.PlasmaMetalCutter.com

    GiantTech Cut40D
    GiantTech Cut50D
    GiantTech CT520D
    GiantTech Tig200s
    GiantTech Arc200
    GiantTech Tig200PACDC
    Miller MM210
    No Brand Chinese Chop Saw
    No Brand Chinese 4" Angle Grinder

  4. #29
    Join Date
    Nov 2007
    Location
    New Hampshire
    Posts
    425
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    What is the horse power rating of your air compressor? If its a 30 gallon tank then its probably no more than than a 6 amp draw. Then the plasma cutter is a Hypertherm 45? if so it draws max current of 28 amps?
    http://www.PlasmaMetalCutter.com

    GiantTech Cut40D
    GiantTech Cut50D
    GiantTech CT520D
    GiantTech Tig200s
    GiantTech Arc200
    GiantTech Tig200PACDC
    Miller MM210
    No Brand Chinese Chop Saw
    No Brand Chinese 4" Angle Grinder

  5. #30
    Join Date
    May 2016
    Location
    Cottonwood, AZ
    Posts
    362
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    There is a 30 amp breaker for the AC, 30 amp breaker for the well pump, a 30 amp breaker for the lights, and a 20 amp breaker for the receptacles. The AC and well pump are a very real load, and will be running often. How could I get a 100 amp subpanel to the shop? I have no space in the main panel, and the subpanel that is feeding the garage subpanel is a 100 amp subpanel itself.
    Hobart Handler 190
    Hypertherm Powermax 45XP
    Lincoln Ranger 305G EFI

  6. #31
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,586
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    The best way to do this is to ignore advice from those who know. Blunder blindly into adversity. You are certain to accidentally find a better way. God be with you.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  7. #32
    Join Date
    Apr 2016
    Location
    CA
    Posts
    12,118
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    So the 100a sub panel that feeds the garage feeds what else other than the garage?
    Lincoln, ESAB, Thermal Dynamics, Victor, Miller, Dewalt, Makita, Kalamzoo. Hand tools, power tools, welding and cutting tools.

  8. #33
    Join Date
    May 2016
    Location
    Cottonwood, AZ
    Posts
    362
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    The whole west wing of the house, so an air conditioner and just basic other stuff, like lights etc
    Hobart Handler 190
    Hypertherm Powermax 45XP
    Lincoln Ranger 305G EFI

  9. #34
    Join Date
    Apr 2016
    Location
    CA
    Posts
    12,118
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Pics of the main and sub's may help in this thread.
    Lincoln, ESAB, Thermal Dynamics, Victor, Miller, Dewalt, Makita, Kalamzoo. Hand tools, power tools, welding and cutting tools.

  10. #35
    Join Date
    Oct 2015
    Posts
    83
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by Louie1961 View Post
    No offense Keith, but you are like 14 years old, right? Where are you going to get the funds for all of this, and do you really need full time electrical service for the welding you do? I would go cheap and make an extension cord to run from the spa sub panel to the garage. At most you would need to have an outlet installed at the sub panel, invest in some 8/2 SOOW, and a set of 6/50 plugs/receptacles for the extension cable. Just turn the spa off when welding. Either that or plug into the existing garage sub panel and turn off enough circuits that it will power your welder.
    I agree. It's considered temp wiring, but hey, if he taps into the load side, I'd have no problem with doing it. It's only one dedicated recpt. The only other way I would do this is going underground with 3 #8 THHN. It's only 50 feet. It's a separate structure so a 60 amp 3R nonfused disconnect would be required on the garage, and then he would come from that into the garage with #6 romex to his recpt. Done deal.

  11. #36
    Join Date
    Jun 2007
    Posts
    197
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    30 amps for the lights?

  12. #37
    Join Date
    Mar 2005
    Location
    Under a Rock
    Posts
    7,979
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by Willie B View Post
    The best way to do this is to ignore advice from those who know. Blunder blindly into adversity. You are certain to accidentally find a better way. God be with you.
    agree.

    Its like the blind leading the blind.

    To Keith Merrell,
    Tell your FATHER to call an electrician and stay out of it. You are over your head.

    It would be a cold day in hell when I let my 14 year old kid start planning the electrical requirements for anything.
    Last edited by John T; 12-02-2018 at 09:27 AM.
    Miller 211
    Hypertherm PM 45
    1961 Lincoln Idealarc 250
    HTP 221


    True Wisdom only comes from Pain.

  13. #38
    Join Date
    Jun 2007
    Posts
    197
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by John T View Post
    agree.

    Its like the blind leading the blind.

    To Keith Merrell,
    Tell your FATHER to call an electrician and stay out of it. You are over your head.

    It would be a cold day in hell when I let my 14 year old kid start planning the electrical requirements for anything.

    Sure glad you was not my Dad...

  14. #39
    Join Date
    Mar 2005
    Location
    Under a Rock
    Posts
    7,979
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by kbeitz View Post
    Sure glad you was not my Dad...
    Me too.

    If I was, I'd be older than moses.
    Miller 211
    Hypertherm PM 45
    1961 Lincoln Idealarc 250
    HTP 221


    True Wisdom only comes from Pain.

  15. #40
    Join Date
    Nov 2007
    Location
    New Hampshire
    Posts
    425
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by Keith Merrell View Post
    There is a 30 amp breaker for the AC, 30 amp breaker for the well pump, a 30 amp breaker for the lights, and a 20 amp breaker for the receptacles. The AC and well pump are a very real load, and will be running often. How could I get a 100 amp subpanel to the shop? I have no space in the main panel, and the subpanel that is feeding the garage subpanel is a 100 amp subpanel itself.
    Well, now that we have known loads.....

    But I question the 30 amp breaker for lights, sounds like its over fused. Also 30 amp for the pump, standard residential would be a 20.

    How big is this building ?

    Anyway being that the AC would be running often then ya you better be asking Dad to open his pockets LOL
    http://www.PlasmaMetalCutter.com

    GiantTech Cut40D
    GiantTech Cut50D
    GiantTech CT520D
    GiantTech Tig200s
    GiantTech Arc200
    GiantTech Tig200PACDC
    Miller MM210
    No Brand Chinese Chop Saw
    No Brand Chinese 4" Angle Grinder

  16. #41
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Another 60 from the main panel should still be doable to run another small sub and take the welder out of it and plenty of reserves for future if the welder load is not being used that is a bunch of extra power considering the 60 sub you already have you should be able to do whatever you need with a combined 120 available. You are likely never going to need more than that would provide. A extra 100 even better but that may not be great idea as if you did find need for using more than 60 out of the 100 you are going to start taxing the main a bit heavily with the 100 sub it already has although we know a good part of that is your existing garage sub panels load also. You would still have to know all the real loads the rest of the service has on it before you can say whether better to add the 60 or a 100. The cost of the wire run would be half on the 60 and if that is all you will ever need it may be better choice for you.

    You did say the main panel was out of breaker space also and that is still a issue ? Often there are ways to solve that depending on what is actually there ?
    Last edited by danielplace; 12-03-2018 at 12:09 PM.

  17. #42
    Join Date
    Jun 2012
    Location
    Laredo + Midland/Odessa
    Posts
    7,132
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by John T View Post
    agree.

    Its like the blind leading the blind.

    To Keith Merrell,
    Tell your FATHER to consult who ever controls the finances in your house to call an electrician and stay out of it. You are over your head.

    It would be a cold day in hell when I let my 14 year old kid start planning the electrical requirements for anything.
    Agreed as well, just added an extra line.

    Keith, Listen to JohnT, and also read between the lines in WillieB's post. You are in over your head.
    1st on WeldingWeb to have a scrolling sig!



  18. #43
    Join Date
    Nov 2009
    Location
    Arizona
    Posts
    3,583
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by danielplace View Post


    Run it all in 1" or 1 1/4" PVC pipe in ground from the house panel/service to the garage and put in a sub panel then install your breaker to feed your outlet then you have a useful panel right there for future. I would not take less than 60 out there and upsize to #4 copper THHN hots #6 neutral and a #10 ground and you'll be golden.
    Are you forgetting about 250.122(B)?
    Miller Challenger 172
    Miller Thunderbolt AC/DC 225/150
    Miller Maxstar 150 STL
    Victor 100C
    Victor Journeyman
    Oxweld OA
    Harris O/A
    Smith O/A little torch

    No, that's not my car.

  19. #44
    Join Date
    Jun 2012
    Location
    Ct
    Posts
    2,801
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by John T View Post
    agree.

    Its like the blind leading the blind.

    To Keith Merrell,
    Tell your FATHER to call an electrician and stay out of it. You are over your head.

    It would be a cold day in hell when I let my 14 year old kid start planning the electrical requirements for anything.
    Hell might be cold, who knows?

  20. #45
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by bigb View Post
    Are you forgetting about 250.122(B)?
    You thinking the ground should be a #8 instead of a #10 since the legs are #4 now.

    Ok. Pull a #8 ground.

  21. #46
    Join Date
    Apr 2017
    Posts
    491
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    If you're going to be giving this kid advice, shouldn't you be a licensed electrician? Kid's only 14, may be smarter than many on ww, but at least he's got enough sense to ask and the only answer he should have been given was to consult an electrician.

  22. #47
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by henry42 View Post
    If you're going to be giving this kid advice, shouldn't you be a licensed electrician? Kid's only 14, may be smarter than many on ww, but at least he's got enough sense to ask and the only answer he should have been given was to consult an electrician.
    Been one of those since July of 1985. This isn't much more than child's play.

    Different world we live in I guess. When I was 14 years old pretty certain I could have wired a friggin' house. That is what I was doing when I was 15.

    First electrical job I did was a 3/4" EMT run 75 feet to a deep 1900 with a 6-50r outlet for a arc welder run out of a 3 phase panel in of huge shop. My dad had bought all the stuff and left for the day when he got back from doing service calls in the afternoon the pipe was run, wire pulled, outlet was in and welder was operational and it was run neat as heck, perfectly level and strapped nicely. I was 12 years old.

  23. #48
    Join Date
    Jan 2015
    Location
    Hamilton Ontario Canada
    Posts
    346
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    danielplace around that age I was welding, driving and doing some electrical. We all forget what we did at that age. Driving was on a farm standard shift standard steering 3/4 ton pickup.
    Welders: IdealArc AC/DC 250
    Lincoln AC 225 converted to AC/DC
    O/A torches
    Lots of Hammers Clamps and Grinders

  24. #49
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,586
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Quote Originally Posted by danielplace View Post
    Been one of those since July of 1985. This isn't much more than child's play.

    Different world we live in I guess. When I was 14 years old pretty certain I could have wired a friggin' house. That is what I was doing when I was 15.

    First electrical job I did was a 3/4" EMT run 75 feet to a deep 1900 with a 6-50r outlet for a arc welder run out of a 3 phase panel in of huge shop. My dad had bought all the stuff and left for the day when he got back from doing service calls in the afternoon the pipe was run, wire pulled, outlet was in and welder was operational and it was run neat as heck, perfectly level and strapped nicely. I was 12 years old.
    My story is similar. Yes. A 14 year old can do this work. A 14 year old who has no prior experience will need more than a couple paragraphs to get it right. I started drawing a paycheck at age 13. I had completed my first year of high school 9th grade. Dad needed help, I needed a job. I took great pride, and was fascinated by the work. That winter, Dad had bought me two Jeeps. One had a drive train, the other had a frame. Neither had a body. I wanted a Jeep so bad, I learned how.

    At 16 I tore down an old house to get cheap building materials. I built a three bay Jeep garage. The electricity was the easy part. I hand dug ditch 60 feet 46" deep through a boulder field. Rocks 4' across came out. The rest of the way was overhead, passed 40 feet through my father's garage that had earlier had only power for lighting. I put 100 amps in that building. It was Mine!

    I had the luxury of training, and a master electrician I could consult twice a day.

    You, daniel, aren't there to coach. With the confidence of youth, supplementing the confidence of some advice, is a deadly combination. A young man could do a lot of harm with your limited advice
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  25. #50
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: How should I run 220 to my shop?

    Never really discussed the details of doing the actual job itself so not sure what you mean by offering advice on which way may or may not be a better way to do it or HAVE it done is a bad idea. If you say so. To me it didn't really seem like he was really looking to do the job as much as what job would be best to do. Maybe that was the plan I don't know. Seems doable to me with a little further instruction and of course with some adult in chare of the house having knowledge of what is happening.

    This is the electric section thought that was kinda the idea aren't we supposed to make suggestions when some one asks opinions of what to do. Anything we discuss could usually get someone in trouble if they weren't smart enough to do whatever it is they are trying to do safely.

    OMG the kid is 14 years old. Some 14 year olds are smarter than many 40 year olds.
    I find it really weird the amount of stuff that gets discussed here and now of a sudden we shouldn't even be talking about it. Did you think he was going to get in over his head ? I mean really we discussed where it could be fed from and ways it could be run I do not think that would be enough to get anyone buying parts at Home Depot.

    Maybe there should be a minimum age limit to enter the dangerous world that lives in this section. Welding though assume is 100% safe for all ages or are we not supposed to discuss anything with anyone that could be a danger to him/herself.

    If you could edit I would just delete all and quit wasting my time here.

    Hey kid don't try this yourself. You could be seriously injured or killed messing around with the electrical.
    Last edited by danielplace; 12-07-2018 at 10:22 PM.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,296,424.61454 seconds with 18 queries