    Re: Miller 211 wiring clarification

    You will not find a 220 volt circuit to connect it to. I'm a bit oversensitive to that subject.
    That said, Inverters are more tolerant of voltage drop, but I can't understand the obsession of new welder owners to undersize power supplies. You buy a new muscle Mustang, but want a lawn mower carburetor, WHY?

    The rules for minimum wire size, and maximum breaker size address fire hazard. They do not address welder performance.

    There is no such thing as too big a wire. Most welders you will encounter are equipped with the same plug. I have probably plugged 20 different welders into the same circuit. Why not install a circuit that'll be useful for numerous welders. You will be surprised, not a big difference in cost.

    My strategy was once #6 copper, 60 amp breaker. Only in two cases was this arrangement not adequate. I once had a Dialarc, I now have a 300/300 Lincoln Idealarc. These needed more power.

    I'm not going to live forever. I refuse to waste time & money upgrading my circuit each time I upgrade my welder.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  2. #52
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    8,879
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Quote Originally Posted by Willie B View Post
    You will not find a 220 volt circuit to connect it to. I'm a bit oversensitive to that subject.
    That said, Inverters are more tolerant of voltage drop, but I can't understand the obsession of new welder owners to undersize power supplies. You buy a new muscle Mustang, but want a lawn mower carburetor, WHY?

    The rules for minimum wire size, and maximum breaker size address fire hazard. They do not address welder performance.

    There is no such thing as too big a wire. Most welders you will encounter are equipped with the same plug. I have probably plugged 20 different welders into the same circuit. Why not install a circuit that'll be useful for numerous welders. You will be surprised, not a big difference in cost.

    My strategy was once #6 copper, 60 amp breaker. Only in two cases was this arrangement not adequate. I once had a Dialarc, I now have a 300/300 Lincoln Idealarc. These needed more power.

    I'm not going to live forever. I refuse to waste time & money upgrading my circuit each time I upgrade my welder.
    Willie, what do you mean by this?
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Klutch 120v Plasma cutter
    SO 2020 bender
    Beer in the fridge

  3. #53
    Join Date
    Mar 2011
    Location
    Western Washington
    Posts
    10,549
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Loosely translated = Go BIG or go home

  4. #54
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Quote Originally Posted by Broccoli1 View Post
    Willie, what do you mean by this?
    Any power company I'm aware of provides 240 volt power.

    That installing the minimum isn't always the least expensive. Go minimum, then switch welders, or even plasma, you might have to upgrade.

    The rules regulating conductor size don't address voltage loss. sometimes, the transformer supplying the power is a long way off. Many inverters will function on a wide range of voltage, but amperage rises. If you begin with a 240 volt at no load circuit, and see voltage loss, you might see amperage rise above specified. A larger conductor might be needed to prevent this.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  5. Likes ronsii liked this post
  6. #55
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    8,879
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    "220, 221 Whatever it takes"



    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Klutch 120v Plasma cutter
    SO 2020 bender
    Beer in the fridge

  7. Likes ronsii liked this post
  8. #56
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    If it comforts you, you annoy me also.

    I've been an electrician 51 years. Most of the people who have tried to tell me they know more than I know, lead with "220". At that moment I can discount everything they say.

    In conversation, Joe Bob uses the phrase, 220 I think little of it. Someone wants to justify connecting a welder using #14 wire, I get suspicious.

    In my life, in my career, I can't easily separate, I have not seen a 220 volt power supply. If you assert yourself as more knowledgeable than me, show me where in this country you get 220 Volt utility power.
    Last edited by Willie B; 02-26-2021 at 08:12 PM.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  9. Likes ronsii liked this post
  10. #57
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    8,879
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Quote Originally Posted by Willie B View Post
    If it comforts you, you annoy me also.

    I've been an electrician 51 years. Most of the people who have tried to tell me they know more than I know, lead with "220". At that moment I can discount everything they say.

    In conversation, Joe Bob uses the phrase, 220 I think little of it. Someone wants to justify connecting a welder using #14 wire, I get suspicious.

    In my life, in my career, I can't easily separate, I have not seen a 220 volt power supply. If you assert yourself as more knowledgeable than me, show me where in this country you get 220 Volt utility power.
    ??

    'tis just humor. 220, 221.


    'taint no one trying to tell you they know more than you, not here at least.
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Klutch 120v Plasma cutter
    SO 2020 bender
    Beer in the fridge

  11. #58
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Quote Originally Posted by Broccoli1 View Post
    ??

    'tis just humor. 220, 221.


    'taint no one trying to tell you they know more than you, not here at least.
    I apologize, I overreacted.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  12. #59
    Join Date
    Feb 2021
    Posts
    3
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Gentlemen,
    Thank you for your insights.

    My concern with running a larger (#6) wire was if there is a "vampire effect" by having such a large conductor. I have #6, You all are telling me that that is fine so I'll run #6, thanks for all of your inputs.

    As for CB, not seeing the logic of running a 60 when Miller recommends 25 (but I don't know for certain). What's the positive of running a 60 vs a 25? What's the negative?


    And while I'm new to this site and new to welding.....I'm not new to life. Sorry to offend by anyone by calling it 220 instead of 240. A ubiquitous term to most Americans, not meant to offend. I suppose a carpenter gets offended when you call a laminate counter formica, which is a copyrighted name.....which lots of us say. Same with aspirin, dixie cup and Hoodsie (for those of us in New England that grew up eating those little mini ice cream cups from Hood Dairy.

    Point is, I was asking a legitimate and pertinent question and used a layman's term - I apologize, I'm sure I'll do it again (I never learn, just ask my wife!).

    If I was being argumentative or confrontational I could understand you calling me out......but I wasn't.

    Thank you for apologizing.....Apology accepted.


    Now......back to our regularly scheduled programming.......

    I want to run a 240V circuit for a Miller 211 with #6 wire.

    What CB? 25A as per Miller or a 60A so I don't have to deal with upgrading the circuit if I get a bigger welder or a Tesla. Is a 60A too big to protect the Millerr 211?

    Thank you.

  13. #60
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Quote Originally Posted by NHWelder View Post
    Gentlemen,
    Thank you for your insights.

    My concern with running a larger (#6) wire was if there is a "vampire effect" by having such a large conductor. I have #6, You all are telling me that that is fine so I'll run #6, thanks for all of your inputs.

    As for CB, not seeing the logic of running a 60 when Miller recommends 25 (but I don't know for certain). What's the positive of running a 60 vs a 25? What's the negative?


    And while I'm new to this site and new to welding.....I'm not new to life. Sorry to offend by anyone by calling it 220 instead of 240. A ubiquitous term to most Americans, not meant to offend. I suppose a carpenter gets offended when you call a laminate counter formica, which is a copyrighted name.....which lots of us say. Same with aspirin, dixie cup and Hoodsie (for those of us in New England that grew up eating those little mini ice cream cups from Hood Dairy.

    Point is, I was asking a legitimate and pertinent question and used a layman's term - I apologize, I'm sure I'll do it again (I never learn, just ask my wife!).

    If I was being argumentative or confrontational I could understand you calling me out......but I wasn't.

    Thank you for apologizing.....Apology accepted.


    Now......back to our regularly scheduled programming.......

    I want to run a 240V circuit for a Miller 211 with #6 wire.

    What CB? 25A as per Miller or a 60A so I don't have to deal with upgrading the circuit if I get a bigger welder or a Tesla. Is a 60A too big to protect the Millerr 211?

    Thank you.
    Either the 25 or the 60 would comply with code. I guess I'd install a 25 or a more common 30. If you change welders, buy a TIG, or a nice plasma, change the breaker then.
    Code allows 200% of I1Eff, so 60 wouldn't be far off, but you don't need that big. No big thing to change later if needed.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  14. Likes NHWelder liked this post
  15. #61
    Join Date
    Feb 2021
    Posts
    3
    Post Thanks / Like

    Re: Miller 211 wiring clarification

    Excellent! Thanks for the prompt response. I'll get on it this week.

    This site is a font of useful information.

    Willie B, I've seen your input on a few different threads, you are knowledgeable and a great resource.....Thank you

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,263,724.72725 seconds with 19 queries