    Circuit and breaker size for Lincoln 360 MP?

    I am new to the forum and am about to purchase a Lincoln Power Mig 360 MP. I have 230 volt, single phase being installed in my garage on a dedicated 125 amp sub-panel. I read in the lincoln owner manual for this unit that it specifies an "Effective Input Amperes" for a 230V circuit single phase power source of 50 amps. Below this the manual then says Recommended Input Wire and Fuse / Single Phase and lists a table with the following:

    Maximum Input Ampere and Duty Cycle - 230/1/50/60 = 83A, 40% (@350amps welder output). The Fuse/Breaker Size is specified at 90A. Extra Hard Usage Input cord is specified at 6. Is it safe to assume:

    1 - short extension cord (25 feet) should be 6 guage wire
    2 - to achieve full output of welder, I need a 50 amp circuit breaker (and associated wire between the subpanel and the receptacle. I had a friend tell me that the 83A rating would be if all the amperage had to go through a single leg of the two hot wires in a 230 v lot circuit.

    Given the specification that effective input amperes are rated at 50, can I use a 50 amp breaker and still get the rated 360 amp output, as the first table seems to indicate?

    Also, if the 50 amp circuit breaker is not what the machine needs, are there receptacles for 90 amp circuits or will I be required to hard wire the unit to the wall/panel, with possibly a wall disconnect switch. Thanks in advance for any advice!

  2. #2
    Join Date
    Jun 2012
    Location
    Big Lake/Monticello MN
    Posts
    15,402
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    The book answered your question, your friend is incorrect.

    Maximum Input Ampere and Duty Cycle - 230/1/50/60 = 83A, 40% (@350amps welder output). The Fuse/Breaker Size is specified at 90A
    Dave J.

    Beware of false knowledge; it is more dangerous than ignorance. ~George Bernard Shaw~

    Syncro 350
    Invertec v250-s
    Thermal Arc 161 and 300
    MM210
    Dialarc
    Tried being normal once, didn't take....I think it was a Tuesday.

  3. #3
    Join Date
    Sep 2020
    Location
    Pacheco, California
    Posts
    21
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    OK, so plan on a 90Amp breaker. Thanks for the quick response! Final question, given the amperage rating of the breaker and the lines to the receptacle, are there 90 amp rated outlets for plugs or do I plan to hard wire the welder to the wall?

  4. #4
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    The cost of a 100 amp plug is very high plus the cost wire.

    I would look at 60 amp plug and wore is a lot lower. I would use slow blow fuses. Breaker will trip faster than a slow blow fuses.

    Dave

    Quote Originally Posted by Chris H View Post
    I am new to the forum and am about to purchase a Lincoln Power Mig 360 MP. I have 230 volt, single phase being installed in my garage on a dedicated 125 amp sub-panel. I read in the lincoln owner manual for this unit that it specifies an "Effective Input Amperes" for a 230V circuit single phase power source of 50 amps. Below this the manual then says Recommended Input Wire and Fuse / Single Phase and lists a table with the following:

    Maximum Input Ampere and Duty Cycle - 230/1/50/60 = 83A, 40% (@350amps welder output). The Fuse/Breaker Size is specified at 90A. Extra Hard Usage Input cord is specified at 6. Is it safe to assume:

    1 - short extension cord (25 feet) should be 6 guage wire
    2 - to achieve full output of welder, I need a 50 amp circuit breaker (and associated wire between the subpanel and the receptacle. I had a friend tell me that the 83A rating would be if all the amperage had to go through a single leg of the two hot wires in a 230 v lot circuit.

    Given the specification that effective input amperes are rated at 50, can I use a 50 amp breaker and still get the rated 360 amp output, as the first table seems to indicate?

    Also, if the 50 amp circuit breaker is not what the machine needs, are there receptacles for 90 amp circuits or will I be required to hard wire the unit to the wall/panel, with possibly a wall disconnect switch. Thanks in advance for any advice!

  5. #5
    Join Date
    Sep 2020
    Location
    Pacheco, California
    Posts
    21
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Dave, thanks! You mentioned a 60 amp plug but should I go ahead and fuse it for the 90 amps? The wiring in the wall will be safe (as I'll run it to code for the 90 amp circuit) but will I potentially fry my plug if I run the welder at its max duty cycle for some of the heavy plate welding I'll be doing? I'll be welding 1/2" and 3/4" plate a fair bit and will probably be switching between Mig and stick depending on the application. I heard the cord to the actual welder uses #6 wire (not sure if that is right but think I also saw this in the manual) and someone told me that they can do this because of the duty cycle being 60% at 330 amps. Seems to make sense but I am definitely not an electrician! Thanks again.

  6. #6
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    The slow blow fuses can take a 3X load for about 20 seconds.

    So a 60 amp would hold a current at 180 amps for 20 seconds. I do not have charts for slow blow fuses on welders.
    But shops in the 1950's and 1960's would use this trick for there welders.

    Dave

    Quote Originally Posted by Chris H View Post
    I am new to the forum and am about to purchase a Lincoln Power Mig 360 MP. I have 230 volt, single phase being installed in my garage on a dedicated 125 amp sub-panel. I read in the lincoln owner manual for this unit that it specifies an "Effective Input Amperes" for a 230V circuit single phase power source of 50 amps. Below this the manual then says Recommended Input Wire and Fuse / Single Phase and lists a table with the following:

    Maximum Input Ampere and Duty Cycle - 230/1/50/60 = 83A, 40% (@350amps welder output). The Fuse/Breaker Size is specified at 90A. Extra Hard Usage Input cord is specified at 6. Is it safe to assume:

    1 - short extension cord (25 feet) should be 6 guage wire
    2 - to achieve full output of welder, I need a 50 amp circuit breaker (and associated wire between the subpanel and the receptacle. I had a friend tell me that the 83A rating would be if all the amperage had to go through a single leg of the two hot wires in a 230 v lot circuit.

    Given the specification that effective input amperes are rated at 50, can I use a 50 amp breaker and still get the rated 360 amp output, as the first table seems to indicate?

    Also, if the 50 amp circuit breaker is not what the machine needs, are there receptacles for 90 amp circuits or will I be required to hard wire the unit to the wall/panel, with possibly a wall disconnect switch. Thanks in advance for any advice!

  7. Likes Chris H liked this post
  8. #7
    Join Date
    Sep 2020
    Location
    Pacheco, California
    Posts
    21
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Thanks! Very helpful indeed.

  9. #8
    Join Date
    Jun 2014
    Posts
    189
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Quote Originally Posted by Chris H View Post
    Dave, thanks! You mentioned a 60 amp plug but should I go ahead and fuse it for the 90 amps? The wiring in the wall will be safe (as I'll run it to code for the 90 amp circuit) but will I potentially fry my plug if I run the welder at its max duty cycle for some of the heavy plate welding I'll be doing? I'll be welding 1/2" and 3/4" plate a fair bit and will probably be switching between Mig and stick depending on the application. I heard the cord to the actual welder uses #6 wire (not sure if that is right but think I also saw this in the manual) and someone told me that they can do this because of the duty cycle being 60% at 330 amps. Seems to make sense but I am definitely not an electrician! Thanks again.
    I would suggest you talk to a licensed electrician verses getting advice from a welding forum or from " someone told me". The manual provides the info you need to make it work.
    Anyone can hook up wires and install a breaker. Whether you destroy a welder, electrocute yourself or burn down a structure due to poor info, its on you. No offense to the members here but from what you have said so far, hire a licensed person that does this kind of stuff for a living.

  10. Likes Chris H liked this post
  11. #9
    Join Date
    Sep 2020
    Location
    Pacheco, California
    Posts
    21
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    I will definitely have a licensed electrician do the install and will put the manual in front of him before he does so. Just talked to one: He confirmed that a 90 amp circuit is what the welder requires to get full amperage capacity and duty cycles out of it and that is the way I will have it wired up. Can't wait to get it all in place and to be able to use the full output without any worries about burning my house down. Thanks all for the input.

  12. #10
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Most license electricians go to a electric engineer.
    Most of today's engineers have little data for this application. You someone that work in the 1950's witch how I came by the information using time delay fuses.
    Odds are they retire 40 years

    Dave

    Quote Originally Posted by kize View Post
    I would suggest you talk to a licensed electrician verses getting advice from a welding forum or from " someone told me". The manual provides the info you need to make it work.
    Anyone can hook up wires and install a breaker. Whether you destroy a welder, electrocute yourself or burn down a structure due to poor info, its on you. No offense to the members here but from what you have said so far, hire a licensed person that does this kind of stuff for a living.

  13. #11
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    The breaker is safety all that happen is breaker would flip
    I would ask him about time delay fuses protection.
    This is what use for motors for starting load and for buss boxs as breakers would flip.

    Dave

    Quote Originally Posted by Chris H View Post
    I will definitely have a licensed electrician do the install and will put the manual in front of him before he does so. Just talked to one: He confirmed that a 90 amp circuit is what the welder requires to get full amperage capacity and duty cycles out of it and that is the way I will have it wired up. Can't wait to get it all in place and to be able to use the full output without any worries about burning my house down. Thanks all for the input.

  14. #12
    Join Date
    Sep 2014
    Posts
    2,372
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Quote Originally Posted by Chris H View Post
    I will definitely have a licensed electrician do the install and will put the manual in front of him before he does so. Just talked to one: He confirmed that a 90 amp circuit is what the welder requires to get full amperage capacity and duty cycles out of it and that is the way I will have it wired up. Can't wait to get it all in place and to be able to use the full output without any worries about burning my house down. Thanks all for the input.
    If you size up everything right, that welder will weld without a problem. The breaker will never trip, the wire will never get warm. I just recently put a 100 amp plug onto my welder it was mad expensive. But the way I use it and move it, it pays. If you are going to have your welder on wheels, you might want to get a #2 AWG SOOW cord and also a basket like for pulling wire and mount that basket near the panel so incase you are moving the welder you do not pull your panel off the wall. It will just take it right off the wall.


    Sincerely,

    William McCormick
    If I wasn't so.....crazy, I wouldn't try to act normal, and you would be afraid.

  15. #13
    Join Date
    Sep 2020
    Location
    Pacheco, California
    Posts
    21
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    William, thank you. Sounds like you are running a similar amp rated machine. I will wire it for the 90 amps and use the two gage wire for the extension cord and a basket, as you suggest. Now I need to source the monster plugs! Do you remember where you got your plugs? I will call a local electrical supply house to see if they stock them.

  16. #14
    Join Date
    Jun 2012
    Location
    Laredo + Midland/Odessa
    Posts
    7,132
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    easy google search

    https://www.elecdirect.com/pin-sleev...YaAhWDEALw_wcB

    https://www.elecdirect.com/pin-sleev...-page-product1

    Or just get the Pro Pulse 300 that you were asking about, and run it off a regular 50A 6-50 style plug/receptacle.
    Last edited by Oscar; 10-04-2020 at 10:21 AM.
    1st on WeldingWeb to have a scrolling sig!



  17. #15
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Quote Originally Posted by Chris H View Post
    William, thank you. Sounds like you are running a similar amp rated machine. I will wire it for the 90 amps and use the two gage wire for the extension cord and a basket, as you suggest. Now I need to source the monster plugs! Do you remember where you got your plugs? I will call a local electrical supply house to see if they stock them.
    They don't stock them that is for sure.
    Forget that idea unless you MUST have them.

    Hardwired with cord or just Greenfield flex is usually the way to go unless you have to unplug it for some reason it really serves no purpose whatsoever.
    Last edited by danielplace; 10-04-2020 at 10:45 AM.

  18. #16
    Join Date
    Mar 2010
    Location
    Ceres, California
    Posts
    4,233
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Only problem with hard wiring is you must have a disconnect at the cord connection.
    If you want a plug look up Meltric plugs they have both a receptacle and a disconnect all in one unit.

  19. #17
    Join Date
    Sep 2020
    Location
    Pacheco, California
    Posts
    21
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Thanks for the tip! I got ahold of the manual and note that the machine is wired with a 50 AMP 3-prong plug. Interesting to see this since the manual notes a max current of 83 amps. Must be for very short durations. I just wired my garage and wired up a dedicated 100 amp circuit with 2 gauge wire and 100 amp breaker in a new sub panel. I also have a 50 amp circuit wired up with standard 6 gauge wire. I think I am set for any eventuality now and have the second circuit for a dedicated tig machine. I think I will save my pennies for the Miller dynasty 400 for that circuit. In the mean time, I will have plenty of fun with the Lincoln 360 MP! Can’t wait to order it. I think I can pull the trigger now that I have the dedicated circuits all wired up. Will post pictures as soon as I have it all hooked up.

  20. #18
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    Quote Originally Posted by ccawgc View Post
    Only problem with hard wiring is you must have a disconnect at the cord connection.
    If you want a plug look up Meltric plugs they have both a receptacle and a disconnect all in one unit.
    Disconnects are cheap and plentiful but not true for most situations as panel is in site. If panel is in site the breaker in the panel can be the disconnect.

  21. #19
    Join Date
    Sep 2020
    Location
    Pacheco, California
    Posts
    21
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    yeah, my sub-panel will be 2 feet behind the welder and unobstructedk for easy access. I think I will go with that option. My circuit is wired with 2 gauge wire and protected with a 100 amp breaker, so I should have adequate protection and capacity in the wire for any likely current draw. I can readily wire in a disconnect if I want to have the extra assurance. Will keep that in my back pocket.

  22. #20
    Join Date
    Mar 2006
    Location
    Yuma, Arizona
    Posts
    3,419
    Post Thanks / Like

    Re: Circuit and breaker size for Lincoln 360 MP?

    I have the Lincoln 350MP and had the Lincoln Precision TIG 275. I just hard wired in an 80amp breaker and proper sized wire. Never had an issue. But as someone has already stated, a 50Amp outlet can be derated for welder use. Usually must be labeled for inspection purposes.

    Also, if you want to get fancy, look up Appleton 100 Amp connectors. We used them at work. Sit down before you look at the price.
    Lincoln Power Mig 210MP MIG
    Lincoln Power Mig 350MP - MIG and Push-Pull
    Lincoln TIG 300-300
    Lincoln Hobby-Weld 110v Thanks JLAMES
    CK TIG TORCH, gas diffuser, pyrex cup
    Thermal Dynamics Cutmaster 101
    My brain

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management