    1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    Tried to use my Miller today and it's tripping out on start up.

    It is also making a hum, it never did before at start up then trips the 50 amp breaker.

    Never had this problem before, also the cord to the outlet and the breaker are fine with my Mig 180, so...

    I'm thinking I have a Welder problem?

    Does anyone here have any ideas on this?

    This Welder is a Beast and not looking forward to taking it to a shop, rather fix it myself, if possible!

    Thanks!!!
    Attached Images Attached Images  

  2. #2
    Join Date
    Jun 2016
    Location
    Back to the jungle
    Posts
    3,993
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Killer rig. You need 60 amps for the breaker. Better to hardwire the thing

  3. Likes Louie1961 liked this post
  4. #3
    Join Date
    Jun 2014
    Location
    Southern Illinois
    Posts
    987
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    The hum and the tripping, my first thought is a rectifier diode. I could be way off but I would research that first


    Sent from my iPhone using Tapatalk
    Steve

    Miller Dialarc 250 (1990)
    Miller Maxstar 140 STR (2003)
    Lincoln SA200 Redface Pipeliner (1966)
    Lincoln MP210 (2015)
    Victor and MECO torches

  5. #4
    Join Date
    Mar 2010
    Location
    Ceres, California
    Posts
    4,233
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    check the weld diodes one might be shorted.

  6. #5
    Join Date
    Jun 2012
    Location
    CT
    Posts
    6,501
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Quote Originally Posted by Bonzoo View Post
    Killer rig. You need 60 amps for the breaker. Better to hardwire the thing

    HOLY SH!T man, I've missed seeing you around here. Welcome back.
    Miller Multimatic 255

  7. #6
    Join Date
    Jun 2012
    Location
    Big Lake/Monticello MN
    Posts
    15,402
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Yep, I'm going with diodes too.

    I popped one while welding once. Machines starts to hum like its fully loaded - dead short.
    Dave J.

    Beware of false knowledge; it is more dangerous than ignorance. ~George Bernard Shaw~

    Syncro 350
    Invertec v250-s
    Thermal Arc 161 and 300
    MM210
    Dialarc
    Tried being normal once, didn't take....I think it was a Tuesday.

  8. #7
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    Thanks everyone, have not got it open yet but had no problem for years, now this.

    I guess if I see nothing, (burnt?) then I will just have to test, all the diodes, and see, if one is bad with the Fluke VOM?

  9. #8
    Join Date
    Jun 2014
    Location
    Southern Illinois
    Posts
    987
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    There is a diode test function on most Fluke meters. Download a manual from Fluke to get the process for checking them


    Sent from my iPhone using Tapatalk
    Steve

    Miller Dialarc 250 (1990)
    Miller Maxstar 140 STR (2003)
    Lincoln SA200 Redface Pipeliner (1966)
    Lincoln MP210 (2015)
    Victor and MECO torches

  10. #9
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Quote Originally Posted by Sparkie1957 View Post
    There is a diode test function on most Fluke meters. Download a manual from Fluke to get the process for checking them


    Sent from my iPhone using Tapatalk

    Hi,
    Thanks, I'll have to find them first, but downloaded the closest Owners Manual from Miller, so should be ok!

  11. #10
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    Ok, opened her up and found 4 Diodes, 2 of each goes to the same terminals...

    Just nutted in on one end and then a wire going to the attachment point, looks easy enough to pull one at the time and test.

    Did not see or smell any burning or something getting hot?

    IF I do find a bad Diode, would you just buy and replace all of them while I'm in there???

  12. #11
    Join Date
    Jun 2014
    Location
    Southern Illinois
    Posts
    987
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    I would suggest looking online, perhaps EBay. They don’t have to come in a Miller bag. There are threads on suitable replacements. I would change them all out


    Sent from my iPhone using Tapatalk
    Steve

    Miller Dialarc 250 (1990)
    Miller Maxstar 140 STR (2003)
    Lincoln SA200 Redface Pipeliner (1966)
    Lincoln MP210 (2015)
    Victor and MECO torches

  13. Likes 12V71 liked this post
  14. #12
    Join Date
    Jun 2012
    Location
    Big Lake/Monticello MN
    Posts
    15,402
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    I agree, change all 4.
    The cheapest cost diodes I've found were on ebay for the DC wind power projects.

    Way cheaper than Miller.
    Dave J.

    Beware of false knowledge; it is more dangerous than ignorance. ~George Bernard Shaw~

    Syncro 350
    Invertec v250-s
    Thermal Arc 161 and 300
    MM210
    Dialarc
    Tried being normal once, didn't take....I think it was a Tuesday.

  15. #13
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    Thanks, will look into that.

    I labeled and tested all 4 diodes, one was bad, so I'm going to put in 4 more!

    Thanks to everyone for the help so far!

  16. #14
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    Found these on EBAY, of course, I know, I need 2 pos and 2 neg polarity.

    They do say these are for Miller Welders, just checking before ordering.

    Is there a certain Diode you guys use???

    https://www.ebay.com/itm/Part-037-30...4AAOSw33FfoCyY

    https://www.ebay.com/itm/Part-037-30...YAAOSwEJdfoC0-

  17. #15
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    I E-Mailed the Seller on EBAY and he told me more about the Diodes as far as size ect.

    Seems a decent company so I ordered 4 new Diodes for about $110...

    That's what Miller wants for one almost.

    Called Digi-Key and got the phone run around.

    The Guy on E-Bay used the same numbers as Miller and there were really no question on if they would work...we will see!

  18. #16
    Join Date
    Jun 2014
    Location
    Southern Illinois
    Posts
    987
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Sounds like a good deal. You’ll have a great welder for many more years when those are installed


    Sent from my iPhone using Tapatalk
    Steve

    Miller Dialarc 250 (1990)
    Miller Maxstar 140 STR (2003)
    Lincoln SA200 Redface Pipeliner (1966)
    Lincoln MP210 (2015)
    Victor and MECO torches

  19. Likes seagiant liked this post
  20. #17
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Quote Originally Posted by Sparkie1957 View Post
    Sounds like a good deal. You’ll have a great welder for many more years when those are installed


    Sent from my iPhone using Tapatalk
    Hi,
    Thanks for the help again, I was Merchant Marine for 40 years and the last 20 in the Engine Room.

    Did a lot of repairs and fabricating...

    Almost every ship I worked on had a big, 3 PH, Lincoln or Miller stick Welder, and with 3 PH and DC, you really had a smooth running machine.

    Saw this Miller Dialarc 250 on CL for $325 and jumped on it.

    Came with 50 ft. Leads a new Stinger and sat on a Miller OEM Iron Wheeled Cart.

    Has worked fine for years, this is the only problem, but it is 40 years old, but...

    She will burn a rod!
    Attached Images Attached Images  

  21. Likes Louie1961 liked this post
  22. #18
    Join Date
    Jun 2014
    Location
    Southern Illinois
    Posts
    987
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    I had a Dialarc 250, I think it was a late 80’s. I restored it and having powder coated and had a custom aluminum diamond tread top bent for it. Great welder!



    Sent from my iPhone using Tapatalk
    Steve

    Miller Dialarc 250 (1990)
    Miller Maxstar 140 STR (2003)
    Lincoln SA200 Redface Pipeliner (1966)
    Lincoln MP210 (2015)
    Victor and MECO torches

  23. Likes seagiant, Louie1961 liked this post
  24. #19
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Quote Originally Posted by Sparkie1957 View Post
    I had a Dialarc 250, I think it was a late 80’s. I restored it and having powder coated and had a custom aluminum diamond tread top bent for it. Great welder!



    Sent from my iPhone using Tapatalk
    Hi,
    NICE!

    I like that top, might have to look into that.

    Those old OEM, Iron Wheel Carts, are the Bomb!!!

  25. #20
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    My Diodes came in, will put them in tomorrow...

    Hope that cures my Welder, we will see!
    Attached Images Attached Images  

  26. #21
    Join Date
    Jun 2014
    Location
    Southern Illinois
    Posts
    987
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Think positive! Then negative! Lol. I’m sure you will have a good welder when your done


    Sent from my iPhone using Tapatalk
    Steve

    Miller Dialarc 250 (1990)
    Miller Maxstar 140 STR (2003)
    Lincoln SA200 Redface Pipeliner (1966)
    Lincoln MP210 (2015)
    Victor and MECO torches

  27. #22
    Join Date
    Sep 2016
    Location
    Detroit, Michigan
    Posts
    1,534
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Quote Originally Posted by seagiant View Post
    Hi,
    My Diodes came in, will put them in tomorrow...

    Hope that cures my Welder, we will see!
    Wow...color coding for current direction....awesome idea! That's way better than a tiny little arrow printed on the side. You may already know this, but you don't want to forget the thermal paste between the diode and where it mounts. It helps the diode dissipate heat better and extends their life. It appears they had a couple of tubes of that in the package, so you should be set.
    Check out my bench vise website:
    http://mivise.com


    Miller Syncrowave 250DX
    Millermatic 350P with XR AlumaPro
    Miller Regency 200 with 22A feeder and Spoolmatic 3
    Hobart Champion Elite
    Everlast PowerTig 210EXT

  28. #23
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    No, the paste was not included, I bought that earlier.

    I labeled everything, so should be a snap!

  29. #24
    Join Date
    May 2015
    Posts
    80
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    Hi,
    Ha! Ha! Ha!...

    Well, the new Diodes are in, and she's running, even more quite, than before...

    All you can hear now is the fan running, and she's not tripping out, of course.

    Admittedly, I don't stick weld everyday, but being able to use different electrodes makes this Miller more versatile than my Mig!

    Thanks to everyone for the help and education, I now know more about Welders, than I really wanted to!!!

    Happy, I was able to take care of it myself, of course!!!

    Oh yea, I was wrong, they did include, a SMALL vial of heat paste!
    Last edited by seagiant; 03-16-2021 at 11:48 AM.

  30. Likes bead-boy, G-ManBart, Louie1961 liked this post
  31. #25
    Join Date
    Jun 2012
    Location
    CT
    Posts
    6,501
    Post Thanks / Like

    Re: 1980 Miller Dial Arc 250, Tripping Breaker At Start Up!!!

    [QUOTE=seagiant;8806731]Admittedly, I don't stick weld everyday, but being able to use different electrodes makes this Miller more versatile than my Mig!/QUOTE]

    Well I might not go that far. A 250 amp MIG is WAY versatile than a 250 amp stick welder, in my opinion. Now if you are talking about a less powerful MIG, then it might be up for debate. ;-)
    Miller Multimatic 255

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,270,209.11071 seconds with 20 queries