    50A circuit question

    hi, i believe i have this figured out but wanted to be sure and wasnt able to find any old posts on it.
    i'm installing a charging station in my garage and it requires a 50A circuit.
    i have space for a 50A breaker as this was for future charging station use but now i need to wire it. it would be about 50' to a NEMA 6-50 outlet so i'm thinking 2 runs of #6 and 1 #8 for ground?
    i dont know if the NEC book is open to the public but i wasnt able to find it online.
    thank you

  2. #2
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by superwelder View Post
    hi, i believe i have this figured out but wanted to be sure and wasnt able to find any old posts on it.
    i'm installing a charging station in my garage and it requires a 50A circuit.
    i have space for a 50A breaker as this was for future charging station use but now i need to wire it. it would be about 50' to a NEMA 6-50 outlet so i'm thinking 2 runs of #6 and 1 #8 for ground?
    i dont know if the NEC book is open to the public but i wasnt able to find it online.
    thank you
    I do not believe you can access NEC online except paying hundreds in subscription service.

    Check terminals. You are limited to terminal temperature rating, and must derate if more than three conductors in conduit, or bundled or if it runs through a hot area. #8 copper is rated at 75 degree C 50 amps. I'd still use #6. You won't be there to react if it were to get hot. Whether you need a center tap conductor check instructions. Equipment ground conductor is #8 minimum.

    You need GFCI protection & wet location if outdoor.

    Use exact conformation in terminating, these are notorious for overheated terminations.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  3. #3
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: 50A circuit question

    If to feed a 6-50 outlet then as you stated your 2 hot #6's are perfect but your ground only needs a #10 and no need for neutral on that outlet. Up to like 50 feet approx.

  4. #4
    Join Date
    May 2006
    Location
    sacramento, ca
    Posts
    294
    Post Thanks / Like

    Re: 50A circuit question

    thank you guys. if i can use #10 for ground that would be great, i have a ton of it haha.
    i understand the equipment ground but if this is a plug (not hardwired) is it considered equipment?
    also, i'll find a calculator but i believe 3/4" conduit would code.

  5. #5
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by superwelder View Post
    thank you guys. if i can use #10 for ground that would be great, i have a ton of it haha.
    i understand the equipment ground but if this is a plug (not hardwired) is it considered equipment?
    also, i'll find a calculator but i believe 3/4" conduit would code.
    If you are talking THHN that'd be fine if no neutral is needed.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  6. #6
    Join Date
    Mar 2018
    Location
    Stokes County, NC
    Posts
    311
    Post Thanks / Like

    Re: 50A circuit question

    The NEC is apparently available online at: https://www.nfpa.org/codes-and-stand...ds/free-access

    EDIT: removed some incorrect GFCI protection info....Thanks, rexcormack! I wish we just had a strike though edit feature and that the darn site didn't limit the time window for edits.




    Lance
    Attached Images Attached Images
    Last edited by LanceR; 04-30-2021 at 08:20 AM.
    Lance

    Multimatic 255 w/MDX-250 EZ-Select gun
    Hypertherm Powermax45 XP
    Heck Bevel Mill 4000
    Miller/Smith heavy duty torch set
    9" Evolution circular saw

  7. Likes albrightree, farmall liked this post
  8. #7
    Join Date
    Dec 2008
    Location
    Lockhart,Tx (BBQ capitol of the world)
    Posts
    1,436
    Post Thanks / Like

    Re: 50A circuit question

    LanceR,
    It says 150 volts or less TO GROUND so a 230 volt circuit would be 115 volts TO GROUND so
    it looks like it would need GFCI if in a wet location.
    WillieB, am I reading that correctly?

  9. #8
    Join Date
    Mar 2018
    Location
    Stokes County, NC
    Posts
    311
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by rexcormack View Post
    LanceR,
    It says 150 volts or less TO GROUND so a 230 volt circuit would be 115 volts TO GROUND so
    it looks like it would need GFCI if in a wet location.
    WillieB, am I reading that correctly?
    Thanks, Rex. I do believe that you are correct. I just edit my post and since we don't have a strike through feature to do that with I removed the incorrect statement. I'd have much rather have left it with the strike through though so you post made more sense to new-comers to the thread.
    Lance

    Multimatic 255 w/MDX-250 EZ-Select gun
    Hypertherm Powermax45 XP
    Heck Bevel Mill 4000
    Miller/Smith heavy duty torch set
    9" Evolution circular saw

  10. #9
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by rexcormack View Post
    LanceR,
    It says 150 volts or less TO GROUND so a 230 volt circuit would be 115 volts TO GROUND so
    it looks like it would need GFCI if in a wet location.
    WillieB, am I reading that correctly?
    That is how I read it. NEC changes are not necessarily adopted by every locality. Here at least NEC may be adopted after lengthy panel examination of code changes. 2020 code was just now adopted in VT with numerous amendments'

    As I understand Outdoor, in a garage, or pretty much all locations.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  11. #10
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

  12. Likes albrightree liked this post
  13. #11
    Join Date
    Sep 2005
    Location
    Cave Creek AZ
    Posts
    3,347
    Post Thanks / Like

    Re: 50A circuit question

    Don’t install a gfci of any sort, it will cause you nothing but problems, it is in a garage, no need to have it, unless you like having a dead battery and enjoy the walk to the circuit box, then by all means put one in.
    The plug on my wifes tesla has a temperature sensor of some sort. I get alerts of high temperature when it is charging for long periods. I have felt it, it feels warm, but not hot. No discernible degradation at the wire connection points. I am likely going to put in the 14-50 that it was originally set up for.
    You would be wise to run a slightly larger conduit, and to add a neutral to your bundle of wires. It won’t cost that much more, but gives you a lot more options in the future.

  14. Likes farmall liked this post
  15. #12
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by walker View Post
    Don’t install a gfci of any sort, it will cause you nothing but problems, it is in a garage, no need to have it, unless you like having a dead battery and enjoy the walk to the circuit box, then by all means put one in.
    The plug on my wifes tesla has a temperature sensor of some sort. I get alerts of high temperature when it is charging for long periods. I have felt it, it feels warm, but not hot. No discernible degradation at the wire connection points. I am likely going to put in the 14-50 that it was originally set up for.
    You would be wise to run a slightly larger conduit, and to add a neutral to your bundle of wires. It won’t cost that much more, but gives you a lot more options in the future.
    EXACTLY what I was thinking about a GFI on a piece of charging equipment. That is something you most likely will regret. Wire it properly and ground it good and let it rip.

    Think about it for a second as we are on a welding forum. Charger is similar to a welder in many ways.

    You wouldn't setup the welder circuits with GFI's. I don't think I would on the charger either.

  16. #13
    Join Date
    May 2006
    Location
    sacramento, ca
    Posts
    294
    Post Thanks / Like

    Re: 50A circuit question

    thanks again guys. i do not plan on using GFCI, like you mentioned, its in the garage and i dont feel like resetting it every couple hours.
    yes i was planning on running THHN but is it different if i do NM-B? i was thinking worse case, if i cant run conduit easily ill just grab a 50' roll of romex. also, actual measurement comes out to 47'.

  17. #14
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by superwelder View Post
    thanks again guys. i do not plan on using GFCI, like you mentioned, its in the garage and i dont feel like resetting it every couple hours.
    yes i was planning on running THHN but is it different if i do NM-B? i was thinking worse case, if i cant run conduit easily ill just grab a 50' roll of romex. also, actual measurement comes out to 47'.
    Same. 6-2 with ground will be 2-# 6 and solid #10 ground. Or as suggested run with 6-3 with ground just in case one day you want a neutral for 120 volt in a subpanel or a new charger that wants one when this model is obsolete.

  18. Likes superwelder liked this post
  19. #15
    Join Date
    May 2006
    Location
    sacramento, ca
    Posts
    294
    Post Thanks / Like

    Re: 50A circuit question

    one more question for you guys.
    i'm not planning on doing this but i've always been curious. say you run a wire from the breaker to a junction box then using wire nuts make another run to another box, does this change anything?
    i know ive see this done on 120v 15A circuits but if your running a 40 or 50A+ circuit to a welder/compressor/dryer do you have to derate the wiring?

  20. #16
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,585
    Post Thanks / Like

    Re: 50A circuit question

    Challenge isn't can you splice, it's how you splice. Normally we try to put high current loads on dedicated circuits. NEC may not define dedicated circuit. To me it means as few connections as possible. There are a dozen electricians on this forum. We won't agree on how to splice. One thing I won't get argument on is a continuous conductor won't have risk inherent in spliced conductor.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  21. Likes superwelder liked this post
  22. #17
    Join Date
    May 2006
    Location
    sacramento, ca
    Posts
    294
    Post Thanks / Like

    Re: 50A circuit question

    i totally agree on that last statement. just curious. i'm not an electrician but theres GOT to be a situation where a dedicated (continuous) conductor isnt possible. right?

  23. #18
    Join Date
    Nov 2009
    Location
    Arizona
    Posts
    3,583
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by superwelder View Post
    i totally agree on that last statement. just curious. i'm not an electrician but theres GOT to be a situation where a dedicated (continuous) conductor isnt possible. right?
    Yes, when you have to transition from one wire type to another, for instance THWN in conduit underground coming up into the wall and switching to NM cable.
    Miller Challenger 172
    Miller Thunderbolt AC/DC 225/150
    Miller Maxstar 150 STL
    Victor 100C
    Victor Journeyman
    Oxweld OA
    Harris O/A
    Smith O/A little torch

    No, that's not my car.

  24. Likes superwelder liked this post
  25. #19
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by superwelder View Post
    i totally agree on that last statement. just curious. i'm not an electrician but theres GOT to be a situation where a dedicated (continuous) conductor isnt possible. right?
    There are often splices made in larger wires every day for all kinds of reasons.

    It is not a problem to splice when done with something with some substance to it designed for high amperage splices. Polaris taps or on of the many other types of rubber/vinyl clad aluminum taps or a compression sleeve crimped with hy press.

  26. Likes superwelder liked this post
  27. #20
    Join Date
    Jul 2020
    Posts
    529
    Post Thanks / Like

    Re: 50A circuit question

    I'm a little late to the party - but just a thought. If you are going through the process to put in that circuit it might be well worth your effort to add 1 more 6g wire for neutral and run a 14-50 outlet. Then adapt from 14-50 to 6-50 between the outlet and the charger.

    This way you have both voltages available there for future use.

    That is what I did here. My old tombstone (round top) came with a range cord on it - NMEA 10-50. So when I set up my inital power cable (from a dryer outlet - 14-30) I wired to a box with a 10-50 for the welder and also put a 5-20r and L14-30r on there. The 5-20 has both horizontal and vertical neutrals so you can use either 5-15 or 5-20. That's my tool plug (drill, grinder, what ever).

    However, when I got my inverter welder it came with a 6-50 plug on it. At the same time I decided to upgrade to a dedicated circuit - new cable, wall mounted outlet (not the dryer circuit). I kept the same theory of the 4 conductor cable, just with 14-50's, with the addition of one more interconnect - at the end of a 25ft extension cord. If I was running a welder alone then yea - the extra neutral/4th wire is useless. But I really like having everything right there at the welder so I can run my 120v gear off the same box. That makes life a lot easier than running a separate extension cord.

    Make sure what ever you "install" is to code - outlet box back to the breaker. Yea, in my case splitting off the 120v and 30a plugs isn't code (they should have separate breakers), but for my uses I'm OK with that - and everything past the wall outlet isn't "installed" anyway - extension cord and the break out box.

    See post 154 for the cabling, 153 has the cord upgrade on the round top welder.
    https://weldingweb.com/vbb/threads/7...47#post8812147

    As far as splicing cables - I don't think that will work very well on bigger cables. You may look in to terminal blocks and putting ring terminals on your wires. For 6 gauge wire that will be a beefy terminal strip and require a substantial box. You're probably not going to make that kind of splice in a 2 gang wall box, for example.

  28. Likes farmall liked this post
  29. #21
    Join Date
    Mar 2018
    Posts
    120
    Post Thanks / Like

    Re: 50A circuit question

    Split bolts are pretty nice for connections with thick wire (larger than ~10 ga).

  30. Likes superwelder liked this post
  31. #22
    Join Date
    Dec 2008
    Location
    Lockhart,Tx (BBQ capitol of the world)
    Posts
    1,436
    Post Thanks / Like

    Re: 50A circuit question

    I've used several of this type splice kit in the past.
    They are well made and work good but they do need some room!

    https://www.morrisproducts.com/pc_pr...9F44E287D7E943

  32. Likes superwelder liked this post
  33. #23
    Join Date
    Nov 2009
    Location
    Arizona
    Posts
    3,583
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by jwmelvin View Post
    Split bolts are pretty nice for connections with thick wire (larger than ~10 ga).
    Yes they are when doing your own work and time is of no consequence, but with today's labor costs split bolts are becoming more or less obsolete as the insulated Polaris type connectors have moved in, quick, easy, minimum skill required and easily reversible.
    Miller Challenger 172
    Miller Thunderbolt AC/DC 225/150
    Miller Maxstar 150 STL
    Victor 100C
    Victor Journeyman
    Oxweld OA
    Harris O/A
    Smith O/A little torch

    No, that's not my car.

  34. #24
    Join Date
    May 2006
    Location
    sacramento, ca
    Posts
    294
    Post Thanks / Like

    Re: 50A circuit question

    so today i took a look at the charger and its actually 14-50. i dont know why i was assuming it was 6-50. i will def do a 6/3.
    thank you

  35. #25
    Join Date
    Mar 2018
    Posts
    120
    Post Thanks / Like

    Re: 50A circuit question

    Quote Originally Posted by bigb View Post
    ... the insulated Polaris type connectors have moved in, quick, easy, minimum skill required and easily reversible.
    Those are neat, thanks. Amazingly expensive it seems, but I hear what you’re saying. I’m glad to know about them.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,257,179.11821 seconds with 20 queries