    Both my welders use a 3 prong plugs. On nice days it would be nice to work under the carport, Where I have a 50 amp 4 prong plug. I have a 4 prong rv cord that Id like to put a 3 prong female plug on. Can someone explain to me how I can wire this?

  2. #2
    Join Date
    Oct 2014
    Posts
    1,187
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    It is apples to apples except the 3 prong will drop the neutral.

    4 wire is 2 hots a neutral and a ground.

    3 wire is just the 2 hots and ground but no neutral.
    Last edited by danielplace; 06-03-2021 at 10:10 PM.

  3. #3
    Join Date
    May 2013
    Location
    South of Dallas
    Posts
    169
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Thank you

  4. #4
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    8,259
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    If you don't want to cut off the RV connector you can buy adapters.

    RVGUARD Welder Adapter Cord 12 Inch, NEMA 14-50P to 6-50R, 50 Amp Welder Adapter, Green

    on Amazon, $30.00
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Klutch 120v Plasma cutter
    SO 2020 bender
    Beer in the fridge

  5. Likes whtbaron liked this post
  6. #5
    Join Date
    May 2013
    Location
    South of Dallas
    Posts
    169
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    The cord I want to use is the twist lock style.

  7. #6
    Join Date
    May 2013
    Location
    South of Dallas
    Posts
    169
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Heres the plug
    Attached Images Attached Images  

  8. #7
    Join Date
    Aug 2019
    Posts
    206
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Quote Originally Posted by Millwrightdude View Post
    The cord I want to use is the twist lock style.
    I rigged the following. Preface, this is for 20 A emergency service off the generator. Got this idea from someone else. I had a second 50 A three prong box that I tied to the 4 prong 20 Nema twist. I braided the chord and tripled the mains to carry well above the 20 A. Works nice. Zero cost.

    Again this is only to have a welder or the carbon arc torch during power outages.

    I can take a better picture if interested

    Regards.

    Name:  0F1CA26F-5D16-448F-B6D6-2B34DA6F9453.jpeg
Views: 206
Size:  514.9 KB

  9. #8
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    8,259
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Quote Originally Posted by Millwrightdude View Post
    Heres the plug
    Do you want to keep the twist lock style connector?
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Klutch 120v Plasma cutter
    SO 2020 bender
    Beer in the fridge

  10. #9
    Join Date
    May 2013
    Location
    South of Dallas
    Posts
    169
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Not really

  11. #10
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    8,259
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Quote Originally Posted by Millwrightdude View Post
    Not really
    Cut that sucker off and put a 6-50 connector on it.

    Red-Hot 1
    Black- Hot 2
    Green- ground

    as Daniel mentioned , don't use the white neutral wire.

    use one of these:

    Forney 58401 Electrical Receptacle, Pin-Type, Portable 50-Amp, 250-Volt,Black
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Klutch 120v Plasma cutter
    SO 2020 bender
    Beer in the fridge

  12. #11
    Join Date
    May 2013
    Location
    South of Dallas
    Posts
    169
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    This is what I have ordered
    Attached Images Attached Images  

  13. Likes Broccoli1 liked this post
  14. #12
    Join Date
    May 2014
    Location
    Manitoba Canada
    Posts
    4,695
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    I went through the same thing with my PTO powered generator, but the 4 prong plug on it wasn't a twistlock. I needed an adapter in a hurry one day to use the buzzbox in the field so I put a 3 prong plugin on a foot of heavy cord with a 4 prong plug in. I've used it numerous times over the years and it's worked well. As mentioned above all you are eliminating is the bare copper ground.... the green, white and black going into your welder cord are still hooked up. I forget offhand whether the white wire goes to the skinny side of the plug or the wide one, but you can usually tell by the color of the screws.
    250 amp Miller DialArc AC/DC Stick
    F-225 amp Forney AC Stick
    230 amp Sears AC Stick
    Lincoln 180C MIG
    Victor Medalist 350 O/A
    Cut 50 Plasma
    Les

  15. #13
    Join Date
    Dec 2007
    Location
    Los Angeles
    Posts
    8,259
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Quote Originally Posted by whtbaron View Post
    I went through the same thing with my PTO powered generator, but the 4 prong plug on it wasn't a twistlock. I needed an adapter in a hurry one day to use the buzzbox in the field so I put a 3 prong plugin on a foot of heavy cord with a 4 prong plug in. I've used it numerous times over the years and it's worked well. As mentioned above all you are eliminating is the bare copper ground.... the green, white and black going into your welder cord are still hooked up. I forget offhand whether the white wire goes to the skinny side of the plug or the wide one, but you can usually tell by the color of the screws.
    I'm not sure what yer saying here though. There are no bare wires in cords.

    He will need the Green Ground wire, Black Hot &
    Red Hot.

    The white neutral wire is the one not used
    Ed Conley
    http://www.screamingbroccoli.com/
    MM252
    MM211 (Sold)
    Passport Plus & Spool gun
    Lincoln SP135 Plus- (Gone to a good home)
    Klutch 120v Plasma cutter
    SO 2020 bender
    Beer in the fridge

  16. #14
    Join Date
    May 2014
    Location
    Manitoba Canada
    Posts
    4,695
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Ahhh.... I used a short chunk of household type wiring because I didn't need it to be flexible.... it was more than 25 yrs ago so my memory might be a little sketchy...
    250 amp Miller DialArc AC/DC Stick
    F-225 amp Forney AC Stick
    230 amp Sears AC Stick
    Lincoln 180C MIG
    Victor Medalist 350 O/A
    Cut 50 Plasma
    Les

  17. #15
    Join Date
    Oct 2014
    Posts
    1,187
    Post Thanks / Like

    Re: 4 prong 50amp to 3 prong 50amp

    Quote Originally Posted by whtbaron View Post
    I went through the same thing with my PTO powered generator, but the 4 prong plug on it wasn't a twistlock. I needed an adapter in a hurry one day to use the buzzbox in the field so I put a 3 prong plugin on a foot of heavy cord with a 4 prong plug in. I've used it numerous times over the years and it's worked well. As mentioned above all you are eliminating is the bare copper ground.... the green, white and black going into your welder cord are still hooked up. I forget offhand whether the white wire goes to the skinny side of the plug or the wide one, but you can usually tell by the color of the screws.
    We are dealing with 240 volt here. The white and the black in a SJ feeding a 240 welder doesn't matter which leg you put either one on. You are going to make it confusing when you don't need too. Wider or narrow blade are one in the same here. Two hots and a ground for 240 welder. The only one you need to place correctly is the green ground or if you used ROMEX or SE that one would be bare.