    This data I have 120 volt welders flipping breakers
    See below

    Dave
    Attached Images Attached Images  
    HF 170 welder
    HF 4x6 band saw
    South Bend 9N
    Mill
    B&D mag drill
    Victor torch

  2. #2
    Join Date
    Jan 2004
    Location
    Brethren, Mi
    Posts
    8,959
    Post Thanks / Like

    Re: 120 Volt Welder user data

    The explanation is ok but I think maybe the moral of the story is they are trying to run too big of wire in the little machines. They can run a bigger wire but are really 023 units.

  3. #3
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    The 120 volt is very limited solid wire with gas 0.023 or 0.030 flux core E71T-GS.
    Forney does say you use a 30 plug witch helps but how has 120 volt 30 amp plug (maybe 4 wire dryer plug), just run 240 volt plug.

    Dave

    Quote Originally Posted by Sberry View Post
    The explanation is ok but I think maybe the moral of the story is they are trying to run too big of wire in the little machines. They can run a bigger wire but are really 023 units.

  4. #4
    Join Date
    Dec 2018
    Location
    Southern California
    Posts
    1,127
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Great info.

    I run a millermatic 211 (inverter) on 120 quite often. Definitely notice more juice out of a bigger breaker and/or thicker wire or cord/closer to breaker.

    It will put out a surprising amount of power on a 10g 30 amp 120 breaker (breaking the rules with nema 15 connectors)

    I've run .035 on 120, not ideal in any sense but it will do what the chart says (3/16") and more in vertical up or with prep, which is more than enough for most repairs that only have 120 access .030 wire is the sweet spot.

  5. #5
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    You like time delay fuses.
    Home type breakers are fast trip type.

    The time delay fuses have a 3x overload for 3 to 5 seconds. This helps on starting a welds and motors. Still protects the wire.

    Dave

    Quote Originally Posted by SlowBlues View Post
    Great info.

    I run a millermatic 211 (inverter) on 120 quite often. Definitely notice more juice out of a bigger breaker and/or thicker wire or cord/closer to breaker.

    It will put out a surprising amount of power on a 10g 30 amp 120 breaker (breaking the rules with nema 15 connectors)

    I've run .035 on 120, not ideal in any sense but it will do what the chart says (3/16") and more in vertical up or with prep, which is more than enough for most repairs that only have 120 access .030 wire is the sweet spot.

  6. Likes Roert42 liked this post
  7. #6
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Quote Originally Posted by SlowBlues View Post
    Great info.

    I run a millermatic 211 (inverter) on 120 quite often. Definitely notice more juice out of a bigger breaker and/or thicker wire or cord/closer to breaker.

    It will put out a surprising amount of power on a 10g 30 amp 120 breaker (breaking the rules with nema 15 connectors)

    I've run .035 on 120, not ideal in any sense but it will do what the chart says (3/16") and more in vertical up or with prep, which is more than enough for most repairs that only have 120 access .030 wire is the sweet spot.
    Here is letter from Forney.

    Dave
    Attached Images Attached Images  
    HF 170 welder
    HF 4x6 band saw
    South Bend 9N
    Mill
    B&D mag drill
    Victor torch

  8. #7
    Join Date
    Nov 2005
    Location
    Nashville, TN
    Posts
    5,897
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Good info. I have been considering/attracted to small 120v migs. Almost bought the HF titanium, but they were out. Recently noticed the century. The century 90 flux core might do what i need.

    I used to have a century 110amp mig. On 30 amp it was really good. Weighed 90lbs not good for portability compared to nowadays
    Last edited by tapwelder; 10-30-2021 at 09:28 PM.

  9. #8
    Join Date
    Jan 2004
    Location
    Brethren, Mi
    Posts
    8,959
    Post Thanks / Like

    Re: 120 Volt Welder user data

    The plug and the wire really isnt much an issue. Its the breaker. These have limited duty cycle. These machines handle 30 ocpd, they are designed for it. The concerns are not with the welder but this is a common recept which allows OTHER tools to be plugged in which are not designed to be used on circuits above 20 a.
    Many/most tools are designed to depend on the breaker for fault protection, the cords, the internals not intended for use on large circuits.
    This is where i get in a bit of trouble on these forums where the focus is all on the wire at the expense of other issues not so apparrent which are as important to circuit design and maybe more so in some cases. If o e notes, the words most/many and general theory as there are a lot of exceptions.

  10. #9
    Join Date
    Jan 2004
    Location
    Brethren, Mi
    Posts
    8,959
    Post Thanks / Like

    Re: 120 Volt Welder user data

    My saw trips a 20 ever few starts.
    Attached Images Attached Images  

  11. #10
    Join Date
    Jan 2004
    Location
    Brethren, Mi
    Posts
    8,959
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Lots of equipment wired 12/30 and most 20A ends in the world installed on 14 cords. May see 14 cords with 30 plugs on special tools in situation like wood shop with multiple machines on the same circuit. Cannot mismatch the recept and the wire though, would need a 10.
    Last edited by Sberry; 10-31-2021 at 12:37 PM.

  12. #11
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Most problems is fast trip breakers.
    It hard to find time delay breaks and when do they very high in cost.
    This why old shops had time delay fuses.
    Still protect the wire but you start motors and welders.

    Dave

    Quote Originally Posted by Sberry View Post
    Lots of equipment wired 12/30 and most 20A ends in the world installed on 14 cords.

  13. #12
    Join Date
    Jan 2004
    Location
    Brethren, Mi
    Posts
    8,959
    Post Thanks / Like

    Re: 120 Volt Welder user data

    They did use time delay fuses and they do make breakers with additional delay but modern breakers do have delay and are not fast like old fuses. They have ai something rating on them making them suitable for motors and heating and cooling equipment.

  14. #13
    Join Date
    Jan 2004
    Location
    Brethren, Mi
    Posts
    8,959
    Post Thanks / Like

    Re: 120 Volt Welder user data

    One of the masters here probably more familiar with the details. I believe it changed somewhere along the way, dont recall when this listing came to be.

  15. #14
    Join Date
    Jan 2004
    Location
    Brethren, Mi
    Posts
    8,959
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Getting rid of fuses in residential was a huge boost to safety. I was in a house not too long ago. Was so old the N had about 3 strands of wire at the weatherhead and all but the furnace was on 2 circuits. Both 30 fuses and by shear luck the combination loads didnt happen to overheat the wire.
    Homeowner said, well the house inspector said this was ok, says it with that look and i had to get his attn and say,,, does this look right 2 u? No connectors, cables wire nutted flying etc.
    Inspector paid by seller instead of buyer. .

  16. #15
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    That ture but to replace fuse people would use penny's.
    Yes you can run motor off of today's breakers but it takes a larger breaker.

    Fuse are still the best protection but people will up size the fuse , use penny and aluminum foil, I even heard of aluminum bars in place of fuses.
    Also if breaker flips you just turn the breaker back on. A fuse blows you are buying a new fuse typically not right size.

    I still use time delay fuses for motor protection today. But I buy the right size.
    Most home owners do not know the correct size.

    Dave

    Quote Originally Posted by Sberry View Post
    Getting rid of fuses in residential was a huge boost to safety. I was in a house not too long ago. Was so old the N had about 3 strands of wire at the weatherhead and all but the furnace was on 2 circuits. Both 30 fuses and by shear luck the combination loads didnt happen to overheat the wire.
    Homeowner said, well the house inspector said this was ok, says it with that look and i had to get his attn and say,,, does this look right 2 u? No connectors, cables wire nutted flying etc.
    Inspector paid by seller instead of buyer. .

  17. #16
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: 120 Volt Welder user data

    That is why they before breakers came to town they required fuse holder reducers installed in fuse panels. You can only put the right size fuse in them once the reducer is installed in the medium E26 socket base and they are non removable. A sharp tang comes out of threaded section that will only allow installation but won't come back out.

  18. #17
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Most had work arounds good news most are afraid of changing a breaker.

    Dave

    Quote Originally Posted by danielplace View Post
    That is why they before breakers came to town they required fuse holder reducers installed in fuse panels. You can only put the right size fuse in them once the reducer is installed in the medium E26 socket base and they are non removable. A sharp tang comes out of threaded section that will only allow installation but won't come back out.

  19. #18
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,586
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Quote Originally Posted by danielplace View Post
    That is why they before breakers came to town they required fuse holder reducers installed in fuse panels. You can only put the right size fuse in them once the reducer is installed in the medium E26 socket base and they are non removable. A sharp tang comes out of threaded section that will only allow installation but won't come back out.
    The Type S fuses I seldom see these days. I hated them! Those who can't read would try to force a 20 to replace a 15 & chip the ceramic thread. Bits of broken thread would jam the female threads in the fuse holder & I'd be in some old lady's overcrowded clothes closet at 90 degrees F picking the bits out by flashlight. Come to think of it, I hate mobile homes in general.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  20. Likes Roert42 liked this post
  21. #19
    Join Date
    Aug 2021
    Posts
    16
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Quote Originally Posted by Sberry View Post
    Lots of equipment wired 12/30 and most 20A ends in the world installed on 14 cords. May see 14 cords with 30 plugs on special tools in situation like wood shop with multiple machines on the same circuit. Cannot mismatch the recept and the wire though, would need a 10.
    Remember that wire has multiple amperage ranges though. 12 gauge is commonly thought of as 20 amp rated but it's actually muuuuch higher in its "open air rating" cheap number 12 has an open air amperage rating of 30 amps...
    Also we all use 15 amp plugs on 20 amp circuits at home if there's more than 1 plug on that circuit... if it's 1 designated plug on the braker it must be rated for the full braker amperage

    Sent from my SM-A426U using Tapatalk

  22. #20
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Here type I like using for motors
    If working I electronics they make a fast blow fuse too.

    Dave

    https://www.bing.com/images/search?q...e+&FORM=HDRSC2

    https://2.bp.blogspot.com/-h6TGaQTTC...se+reponse.png

    Quote Originally Posted by Willie B View Post
    The Type S fuses I seldom see these days. I hated them! Those who can't read would try to force a 20 to replace a 15 & chip the ceramic thread. Bits of broken thread would jam the female threads in the fuse holder & I'd be in some old lady's overcrowded clothes closet at 90 degrees F picking the bits out by flashlight. Come to think of it, I hate mobile homes in general.

  23. #21
    Join Date
    Dec 2013
    Location
    Mount Tabor VT
    Posts
    10,586
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Quote Originally Posted by Slowxj View Post
    Remember that wire has multiple amperage ranges though. 12 gauge is commonly thought of as 20 amp rated but it's actually muuuuch higher in its "open air rating" cheap number 12 has an open air amperage rating of 30 amps...
    Also we all use 15 amp plugs on 20 amp circuits at home if there's more than 1 plug on that circuit... if it's 1 designated plug on the braker it must be rated for the full braker amperage

    Sent from my SM-A426U using Tapatalk
    Always somebody complaining about a cord on a machine or welder being too small, therefore Why do I need heavier wire for the circuit?

    Manufactured items need only laboratory approval. In a bench test, did it overheat? Most of these cords are rated 105 degrees, or even higher. Welders (for example), have limited duty cycle. Following duty cycle rules, it won't overheat.

    The circuit supplying your machine must comply with electrical code. Once we used type NM cable or TW single conductor in conduit rated 60 degrees C. it was (sometimes) rated 15 amps for #14, 20 amps for #12, 30 amps for #10.

    When 90 degree insulation became mainstream, amp ratings rose sharply, but breaker sizes did not. Now, up to 9 conductors can carry traditional amperage in conduit if you don't have to adjust for ambient temperature.
    An optimist is usually wrong, and when the unexpected happens is unprepared. A pessimist is usually right, when wrong, is delighted, and well prepared.

  24. #22
    Join Date
    Aug 2021
    Posts
    16
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Aren't breakers still rated at 60c instead of 90? That's one of those things that bugs me...
    Also why my old house (new to me) had an 85 amp breaker feeding number 6 that was technically rated for that amperage... issue was the breaker wouldn't take the heat so I reduced it to a 50 (had one on hand)

    Sent from my SM-A426U using Tapatalk

  25. #23
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Technical there lot ways to protect wires or electronics. Even most electrician do not know the subject that well.

    Dave

    Quote Originally Posted by Slowxj View Post
    Aren't breakers still rated at 60c instead of 90? That's one of those things that bugs me...
    Also why my old house (new to me) had an 85 amp breaker feeding number 6 that was technically rated for that amperage... issue was the breaker wouldn't take the heat so I reduced it to a 50 (had one on hand)

    Sent from my SM-A426U using Tapatalk

  26. #24
    Join Date
    Oct 2014
    Posts
    2,135
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Quote Originally Posted by Willie B View Post
    Always somebody complaining about a cord on a machine or welder being too small, therefore Why do I need heavier wire for the circuit?

    Manufactured items need only laboratory approval. In a bench test, did it overheat? Most of these cords are rated 105 degrees, or even higher. Welders (for example), have limited duty cycle. Following duty cycle rules, it won't overheat.

    The circuit supplying your machine must comply with electrical code. Once we used type NM cable or TW single conductor in conduit rated 60 degrees C. it was (sometimes) rated 15 amps for #14, 20 amps for #12, 30 amps for #10.

    When 90 degree insulation became mainstream, amp ratings rose sharply, but breaker sizes did not. Now, up to 9 conductors can carry traditional amperage in conduit if you don't have to adjust for ambient temperature.
    The cord length has the most to do with. Look at the element in a 20amp glass fuse. It can be that thin/small even out of easily melted material for the very short distance in the reduced section of the fuse link. The attached cords are skinny because they are short.

    Most of the wiring in any given equipment is going to be much less than the wire the branch circuit uses to feed it so all that wire is grossly over powered but it can't draw more than it's size because each are only feeding a part of the unit like say a single burner in a range so no way that burner can draw much more than the rating it is. A dead short in a short length of 16 gauge will still trip a 50 amp breaker.

    Quote Originally Posted by Slowxj View Post
    Aren't breakers still rated at 60c instead of 90? That's one of those things that bugs me...
    Also why my old house (new to me) had an 85 amp breaker feeding number 6 that was technically rated for that amperage... issue was the breaker wouldn't take the heat so I reduced it to a 50 (had one on hand)

    Sent from my SM-A426U using Tapatalk
    The breakers today and most terminations are rated at 75°C

    This always trumps the rating of the wire. Once you land even a 90°C rated wire in a breaker or lug it can only be used at 75°C ampacity tables if that is rating of breaker/lug.
    Last edited by danielplace; 11-02-2021 at 11:33 AM.

  27. #25
    Join Date
    Mar 2018
    Location
    Clovis California
    Posts
    9,894
    Post Thanks / Like

    Re: 120 Volt Welder user data

    Glass fuses are fast blow type.

    Dave

    Quote Originally Posted by danielplace View Post
    The cord length has the most to do with. Look at the element in a 20amp glass fuse. It can be that thin/small even out of easily melted material for the very short distance in the reduced section of the fuse link. The attached cords are skinny because they are short.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

A) Welding/Fabrication Shop
B) Plant/Production Line
C) Infrastructure/Construction/Repair or Maintenance/Field Work
D) Distributor of Welding Supplies or Gases
E) College/School/University
F) Work Out of Home

A) Corporate Executive/Management
B) Operations Management
C) Engineering Management
D) Educator/Student
E) Retired
F) Hobbyist

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Page generated in 1,713,271,881.78171 seconds with 20 queries